elv / lv afloat
24 Nov 2004
new requirements for fishing vessels.
I am slightly perplexed, it seems that 4.8.2.3 indicates that we may be able to use eg a 48V test for a nominally 24VDC distribution arrangement as found on most fishing boats. or a 24V test for a nominally 12V vessel. But this would be in contradiction of 4.8.2.2 test shall use 500VDC.
My megger only goes as low as 250V for an insulation test. are there 24V insualtion testers?
The BS 7671:2008 said we needed RCD protection, it did not say except for SELV. It is clear there is no point having RCD protection with SELV some times we need to use common sense.
Fair enough, common sense.
I understand that "the possibility of damage" pertains to sensitive equipment such as computers, radio gear, radar, sounders etc that may well be permanently connected. In the case of a standard 24V DC workboat, I would expect older equipment to be rated max 32V (from memory, older wide-voltage stuff usually states 12-32V) and modern gear 10-40V.
twice 24V = 48V, so a possibility of damage to eqpt remains if testing at this level. (?)
I feel that it is common sense to disconnect the actual gadgets when making insulation tests, so why not just make that the damage caveat. just from hard experience I feel that pressurising a soggy 24V wiring at 48V is still not going to reveal any weak spots, which is why the Megger(tm) goes orders of magnitude higher.
maybe Im missing something?
Why do you IR test a 24v install?
What is the likely result of insulation failing at that voltage?
I doubt it's going to give anyone a shock?
It's saying test at 500VDC unless damage is likely, in which case it is acceptable to test at a lower voltage so long as it meets the alternate requirement for insulation resistance
Once in proximity to sea water, all bets are off. Remember we're just a bag of salty water and other bits, which has a low impedance. The skin is high enough impedance that we are generally protected from ELV electric shock, but if you are in sea water that no longer applies.
must admit I hadnt really considered that. most people can certainly feel 24V if you are up to your waist in seawater but it's only uncomfortable, I wouldnt describe it as a shock. No idea what it would be like if you were up to your neck, I guess it could start to become dangerous then.
I thought this requirement was more of an anti-fire precaution, or simply a precaution against emergency equipment not working because of failing supply system.
Actually I had it slightly incorrect, the risk is higher with freshwater, since you apparently only need a voltage gradient of 6V/m to result in electric shock drowning. It's much more difficult to get that kind of gradient in salt water since it has a much lower impedance.
The usual effect is some muscle paralysis rather than cardiac arrest, so technically you don't die from electric shock.