RCD tripped then MCB
25 Jan 2010
Bristol
Tripped the RCD on a split load consumer unit swapping out a socket, earth and Neutral touched.The circuit had its breaker off and is a radial.
However another circuit breaker tripped at the same time as the rcd...this breaker is on the same rcd.
Powered both circuits up with no issues...
So any ideas why an rcd trip would take out another mcb ?
I have RCBOs
Sometimes, if one trips, one or more others also trip.
Sometimes it might be due to lightening.
Sometimes, no cause found.
Check the main earth. Cant the power back flow on a tns system with a break in the earth?
Blup
Yes I had two rather old RCD's and resetting one would often trip the other one, there have been claims by some manufacturers to have cured the problem, seem to remember the Eaton X-Pole was one, and included a warning device to show when getting near to the tripping current.
Today we seem more aware of types of RCD, the AC seems to have now nearly gone, although all my RCBO's are type AC even when they said type B on the box. In the main we used type A, there is also type F and B. The types are because some equipment can either inhibit them tripping or make them more sensitive.
I used an oscilloscope in university, but it is not really as yet part of the electricians tool kit, my test was to measure the loop impedance, if the RCD tripped then must be close to the limit, as the tester used 9 mA to test, so if it held in, I knew I had 9 mA to spare.
What we should do is measure each circuit and the tripping current should be less than 1/3 of the RCD rating, so for a 30 mA 9 mA is the limit, however only in the last year have I had a clamp on ammeter which could measure that. My clamp on before that only measured down to 0.01 amp.
Back in 2008 the regulations said "Every installation shall be divided into circuits, as necessary, to reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation." but people were still fitting duel RCD consumer units, it also said "avoid hazards and minimise inconvenience in the event of a fault" and so one should not have lights and sockets on the same circuit, but people seem to want to read into the regulations what they want to do.
"Circuit. An assembly of electrical equipment supplied from the same origin and protected against over current by the same protective device(s)." "Residual current device (RCD). A mechanical switching device or association of devices intended to cause the
opening of the contacts when the residual current attains a given value under specified conditions." it seemed plain to me back in 2008 that a RCD formed a circuit, so the rules on dividing the installation into circuits was applied to RCD's back in 2008, however people selected not to read the regulations that way. Seems electricians taught about electrics, but not so much on English comprehension a subject I hated at school.
But down to nitty gritty and it's price, we weigh up the cost of a freezer full of food against the price of fitting all RCBO's and many home owners seem to prefer to take a chance if it trips they will find it in time so food not lost, so we are talking about risk assessment. The problem is who pays, loose a freezer full of food, and we claim off insurance, also it is up to the home owner, not the electrician, this has been made plain with the SPD (surge protection device) it is not required for safety, it is required to stop damage to electronic devices connected direct to the mains supply, so the home owner can elect to take the risk.
The rub comes in that the electrician needs to explain to the home owner the risk, and to be frank I am not sure what the risk is, so how can I tell Joe public what the risk is? Default is fit one, but if the home owner says no, then we don't need to fit one. So the same splitting the installation into more or less circuits, I lived in a caravan at one point and all went through one RCD, but to be fair lights were 12 volt from a battery, and the reason we have leakage is AC can transfer by inductive and capacitive linking, so the more cable used the greater the leakage, and a caravan is small. It also means the insulation tester VC60B.jpg only shows faults, as it tests with DC, to measure back ground leakage we need the clamp on ammeter Testing for live.jpg and I have already admitted up until 12 months ago I could not have tested how much earth leakage there was as my meter did not measure that low, and a normal ammeter is no good as can't measure the difference between line and neutral.
We should according to the IET have an EICR done every 10 years, the government requires every 5 years with rental property, but I know I have not fully tested this house, OK I will retest any circuit I have worked on, but I have only really tested my own house to show my son how it is done. He is now also an electrician.
So the big question, are you prepared to pay for all RCBO's to be fitted? Seem to remember when I got the bits for my son to fit for me, cost around £300 and that is without labour costs of course, with a consumer unit change it will cost around £200 extra to have all RCBO's which is less than a freezer full of food, but once changed to then swap to all RCBO it is going to cost more like £800, so is it worth it? As said it is a risk assessment.
@ericmark, I have two rentals with RCBO's, the MK one kept tripping odd RCBO's with no pattern, 32amp one week, 6 amp the next..the arc fault was diagnosed to be "not within tolerance" - whatever that means....since its replacement no trips.
As for a freezer, if ours had more than £50 quids worth in it I would be surprised, its all veg and ice cream, meat and fish never goes near it, put off by extreme food poisoning from my mother in law freezer dregs..she didn't quite understand that a freezer only slows decay its not a time machine. 3 year old salmon for boxing day...that was fun.
Retested the fault this morning, trip the mcb for the 20amp radial, touch the N and E and as expected the RCB trips and the same next door MCB pops off. Disconnected the live from the tripping MCB and retested...Bing off it popped. So swapped the position of the trip happy mcb away from the rcb and no trip....seems the mcb does not like being next to the RCB, I can only assume that the RCB when it trips throws out an electromagnetic field and causes the mcb to trip....the one that has taken the trip happy one's place does not trip. So swapped them back and bang off it goes. Did a quick check of the appliances plugged in to that circuit, found that the laser printer stayed energised for about a minute..disconnected the laser an retested...no trip.
So all I can deduce is that some combination of the laser printer back feeding some sort of induced load and the RCB tripping is enough to pop the mcb...
just very strange..