Hi All
This is the set-up:
5 beds, victorian, ~1800 sqft, 12 radiators (including 3 towel rads, one in each bathroom / en-suite). Vaillant ecotec 637 plus S-plan.
There was weirdly an additional grundfos pump ups2 on top of the internal pump in the boiler. This pump is disconnected so only the internal remains (all rads get hot anyway).
Estimated rads output is ~17 kw, average of 3 online calculators. These are the dimensions:
Temp differential: all rads fully open, boiler ramping up, ~ 10 degrees difference. When all the rads are warm (okay to touch but not for long, seems right temp) the return temp starts to go up and the differential will stabilise at 8/5 degrees. If some rads are closed (e.g. guest room, office) then the differential will be no more than 5 degrees (ie 68 flow, 63 return).
No cycling, although 37 kw/h is massive the boiler can stay on modulating at minimum output with enough rads on, so that's not the issue. Also the rads do get hot as mentioned.
On DHW it's a similar result. The cylinder is 5m from boiler and fairly recent (Zircon 250l, 7y old), flow is at 75 degrees and it will come back at 70 after going through the coil.
Internal boiler pump is on auto for DHW which is almost always at 15%. For DHW it goes the pump value is at 70%.
The house take hours to heat but to be fair it's -2 outside at night the days.
Regarding pipe work, it is 22mm downstairs where the new boiler / cylinder cupboard was set-up 7 years ago. Where the rads are it looks like this:
(Unsure if this is single or double pipe circuit.)
In your opinion what is the reason why there is only a 5 degrees differential, and how can the situation be improved?
This is the set-up: