Tails from inverter to consumer unit
  • Thread starter Thread starter RCZ
  • Start date Start date
RCZ
3 Dec 2024
France
…can the tails going into the consumer unit from the inverter, go straight into the main switch rather than a MCB…I can’t see it makes any difference…thanks
The design of the installation has to ensure that the output from the invertor cannot under any circumstances reach the incoming electrical supply.
One reason for this is to prevent engineers who have turned OFF the local power supply from receiving an electric shock from the invertor that has become connected to the local network.
Thanks Bernard….I understand what you’re saying but I don’t understand the logic….wherever you connect an inverter to a consumer unit in a solar installation, it’s going to make contact with the incoming mains supply. You don’t disconnect the mains supply when the solar power is suppling energy to the consumer unit and your house?! I’m obviously missing something…
Err inverters shut down when the grid feed is not present . If you have a grid tie then then inverter is constantly exporting solar when the demand is less than the supply, which the op does as his solar is connected to the consumer unit.
There seems to be a massive misunderstanding between a system with island mode - ie powers the house when the grid is out and standard solar that just cuts the kw drawn from the grid.
The fuse is there as it protects the cable going to / from the inverter like any other cable in your house.
How will you protect the cables from the main switch to inverter? The only fuse would be the main incoming DNO fuse at maybe 100A?
Much easier to use an MCB. It cant be on a shared RCD though.
What inverter, what design of consumer unit etc. I not France so may not be the same as UK, but the question has been answered even though in the initial question there was not reference to the supply being from any other source,
This says you do intend to interconnect two supplies, however I note on my inverter it needs setting for the country, and you can't expect an answer on to British forum to automatically apply to France.
There are a number of things required.
1) Automatic disconnection of solar panels from the DNO supply should the DNO supply fail.
2) If the DNO supply fails then earth and neutral require bonding, but also they must not be bonded if the supply is good.
3) There needs to be an earth which does not rely on the DNO supply.
How this is done varies, and my inverter has a load of DIP switches to set it for the country being used in.
Since my inverter can only supply 5 kW the UPS is a different supply to the rest of the house, so with loss of DNO supply most of the house will lose power, so the neutral to earth bonding is only for the UPS supply, and the UPS supply in my case does not connect to the consumer unit, I have just one FCU and two double sockets from the UPS.
There is also the problem with uni-directional and bi-directional automatic disconnection devices, which would stop being able to connect the solar inverter to a standard consumer unit, again it will depend on the design of parts which are used in the consumer unit.
General statements without some more information are pointless.
I know what you are trying to say, but the whole idea of exporting solar power could not happen if that were true, no one has said what type of inverter, there is simply not enough information, and even if there was more information, I know France has a different way of supplying private homes, with a lot more split phase than found here in the UK, and also often 16 amp supplies where in the UK rare for it to be under 60 amp.
It was 1980 when I worked on old French supplies, so some what dated, but I know enough not to expect French rules to be same as UK, often their MCB are two pole for example.
If there are people on here who do know the French system then OK lets hear from them, but I would not try to tell some one how to do things in another country except in very general terms, and although I have worked abroad, it was 30 years ago, so things may have changed.
In general, inverters of domestic scale can be divided into three categories.
1. Standalone inverters.
2. Plain grid tie inverters
3. Grid tie inverters with island/backup power support.
A standalone inverter should never be connected to the grid. If a system is intended to be supplied both from the grid and from a standalone inverter then an appropriate transfer switch or interlock must be provided.
A plain grid tie inverter must be connected to the grid to operate, there are some subtleties but it's wired up in much the same way as a load. The circuit feeding it should have appropriate over-current protection and isolation. The downside of such an inverter is that if the power goes out, the inverter shuts down. Even if you have solar/battery power available you can't use it.
A grid tie inverter with island/backup power support, usually requires the power feed for loads requring backup power to run through the inverter. Again any wiring should have appropriate overcurrent protection, though the rating of such may be considerablly higher than for a plain grid tie inverter.
@plugwash does make a good point, the three types of inverter he lists, would require different answers, years ago on a narrow boat my son used the inverter as an isolator from the shore supply, the supply went through a charger class II to the batteries, and from batteries to the inverter, 3 kW with 6 kW peak, so the boats earth was not connected to the shore earth, to save the sacrificial cathodes from needing replacing so often.
And in this case the inverter did feed the consumer unit directly. There are so many variations on the use of inverters, if asked about a LXP HYBRID INVERTER for example you can down load the instructions, and see how it is set up. 1733394582898.png gives the country set up, and really for the answer it needs to be asked on a French forum.
Understand it’s difficult to give a definitive answer, perhaps this schematic will throw some light on it….this is my installation and the tails from the AC unit are not going to the MCBs….the main difference I found here is there is no ring mains, only spurs and each white goods has it’s own spur. The inverter is ONDULEUR HYBRIDE 6KW - DUAL MPPT - HYD 6000-EP - SOFAR
So you have a grid tie to edf and no auto isolation, so your install will turn off if the grid supply fails..... you still need an mcb to protect the cable from the solar install... the edf grid tie will have a fuse/mcb so should your own micro generation from solar.
Imagine if that battery stack had a fault and dumped to your consumer unit....with no mcb - feu feu feu