- Joined
- 25 Apr 2023
- Messages
- 9,274
- Reaction score
- 6,369
- Country
You could try but why would anyone bother....best to get someone on board first.I was planning to leave all the channels and boxes open, conduit in place
Others may disagree.
Is a ring an appropriate and considered choice for this installation?installing a new ground floor ring main in a block built house.
That layout does seam to suit a ring ok
But even I would struggle to justify a ring for one living room.
Running it off a radial with 20A mcb will be fine.
What is the tv socket mounted on ?
Why? Horizontal chases except past doors?OK 10 drops,
OK 10 drops, so around 5 foot each so 100 foot, then add the around the room distance another 50 foot, and also the 1/3 rule for drilling beams may add to that, so looking at around the 200 foot, or around the 60 to 70 meters of cable.
With a ring final with 32 amp MCB allowed 106 meters so that's OK, with 20 amp radial in 2.5 mm² 32 meters, so single radial is out, even with 16 amp, 42 meters still not good enough, so would need to use 4 mm² so then at 20 amp 56 meters so still not really going to work so 16 amp with 4 mm² 72 meters so just about.
So yes only sensible option is a ring final. This is the design stage, and you still need to sign for the design if you have done the design.
Or corners, so 6 drops instead of 10, but have not included the cable used to comply with the 1/3 rules for drilling beams, however at ceiling height there is a safe zone, so there are ways around the 1/3 rule.Why? Horizontal chases except past doors?
Of course they are if there is an accessory on both sides.Horizontal chases around corners are not permitted,