Yes and for the overall drop from the flow and return you should be achieving a delta T of 20C.The boiler is a condensing boiler so would that still be 12 degrees
Open that up by 1/4 from the LS valve.Then work your way to the next radiator.I've got a small rad on the landing and that one seems to heat up first
Is the overall drop the difference in the flow and return should be 20c on the boilerYes and for the overall drop from the flow and return you should be achieving a delta T of 20C.
I wouldnt get to hung up on getting the delta t to 20c, not many modulating boilers manage that at 60c flow. Just get the return temp as low as possible.Is the de
Ok cheers so if I just try and get the flow and return on the rads to 12 degrees the just check the return temp on the boiler and see what it isI wouldnt get to hung up on getting the delta t to 20c, not many modulating boilers manage that at 60c flow. Just get the return temp as low as possible.
Try at least getting a return temperature of lower than 54C.Is the de
Would it be better if I set the flow temp higherTry at least getting a return temperature of lower than 54C.
With your set temp at 60, a drop of 20 degrees will make the return temperature 40c which will achieve condensing.
The higher the flow temperature the more harder it is to achieve a lower temperature to allow the boiler to condense.Would it be better if I set the flow temp higher
Up to 65 degrees (with a 20 degrees drop) will result in a 45 degree return temperature which still will condense.
It all depends on your system but having the temp set no more than 70C is best.
Ok thanks will try and balance the radiators first does it make it harder to balance as its 8mm microbore pipe going to the radiatorsDon't worry about the boiler temperatures for now, just balance the system so that the radiators heat equally and after that you can check on the return temperatures.