Greetings. Having studied many of the threads on here replacing the Lifestyle LP241, I decided to buy a dual channel Hive receiver + Thermostat and replace my LP241.
Hive version - Hive Thermostat for Heating & Hot Water Control (Conventional Boilers), With Hive Nano 3 Hub, White, A Conventional Boiler is Required
On the LP241 programmer terminal block, the connections were N, L, HW off, HW on and CH on. There was NO connection for CH off (Pin2). I did a 1:1 wire swap on the Hive unit.
I traced the mechanical thermostat wiring back to the wiring box in my airing cupboard and linked the wires together with a short piece of wire (so linked together on the terminal block and wires open circuit where the thermostat was.
Everything sort of works.. HW works fine however CH will only come on if HW is on. So if I press the CH button the on the Hive control unit (turning green) nothing happens unless I press the HW button at which point the boiler fires up and radiators come on. As soon as I turn off HW the boiler shuts down???
I did an AI query which suggested I had the Hive in the wrong mode but I think green means pump mode which is correct and I had already shorted out the thermostat (before I did this, I temporarily set the mechanical thermostat to the maximum 30degC). The final suggestion was a faulty micro switch on the 3-way valve, although that would be a coincidence that the switch failed at the same time as swapping over to the Hive unit. I do however have a spare Honeywell 3-way valve I could use. Luckily, i fitted one one where you can separate the motorised head from the brass valve some years ago, so it would be easy to unwire the current version and swap it with a new one.
I wonder if some wiser folk on here have any suggestions??
Cheers John
Sounds like a wiring fault. Can you post a photo of the Hive wiring?
OK Here are photos of the original LP241 plate (I had removed the three L wires), The Hive plate and the mess of wiring in the junction box :(
Ok, first set the existing mechanical thermostat to maximum and see if this operates it independently. If this does, then you have found your issue, I suspect the link is wrong. If this doesn’t work, then I think it’s the hot water off connection could be wrong.
Ok so when I fitted the hive control unit, the original mechanical thermostat was still connected and I set it to 30degC (ie maximum). This when I realized that the CH would only come on when the HW was set to on. I then shorted out the thermostat at the terminal box without making any difference.
I might refit the LP241 and with the old thermostat shorted, should give HW and CH continuously when set to on.
I could try swapping the 3-way valve
Failing all that I will try and find a complete circuit for the system ie control box, pump, 3-way valve and thermostat and trace all the wiring back to the terminal box labelling each wire and ensuring that they go to the correct position.
I'm fairly sure everything was working fine before swapping the LP241 control unit to the Hive one. And I took the photo of the terminal connector before I took the other wires off, so I know that the wiring hasn't changed. I've recovered the original LP241 so I might put that back in place of the Hive and see how it functions. With the old thermostat removed and (shorted out in the terminal box) this will just mean that the CH will remain on continuously when turned on. If everything works fine by replacing the LP241 then it's an issue with the Hive unit. If it still isn't working as expected then maybe the micro switch on the 3-way valve is faulty and not firing up the boiler when CH is enabled.
The central heating system has three modes.
1) DHW only boiler gets power from the tank thermostat, valve at rest.
2) DHW and CH boiler gets power from the tank thermostat, valve at centre position.
3) CH only boiler gets power from the orange wire out of the valve, and valve all the way across.
So, which you describe tends to point to the three port valve or the orange wire from it.
So to motor valve all the way, the grey wire from the tank thermostat needs to be line, or the DHW off from the Hive needs to be live, so you have two ways to motor the valve all the way, so does the CH fail both when switched off, and when tank thermostat satisfied?
OK managed to measure voltages (All AC voltages) this evening :)
HW + CW Both on (Boiler On). Orange = 240V, White = 240V, Grey = 0V
HW Only On. (Boiler On) Orange = 240V, White = 28V, Grey = 0V
CH Only On (Boiler off??). Orange = 0V, White = 240V, Grey = 15V
These are what you should have, so something is amiss
So here's the problem.
When CH only is required there should be 240v on the white (CH on) and grey (HW off). Both are required to be 240v to wind the valve over to the CH only position when it operates a microswitch that puts 240v on the orange wire and the boiler starts.
You seem to be lacking the HW off signal
Interesting !!! so there is definitely a HW off connection on the controller terminal block. I wonder if there is a problem with the Hive unit? I will temporarily re-fit the LP241 controller and see what that does (CH should be on continuously as I shorted out the thermostat in the wiring box)
'HW off' comes from two places:
1. Programmer (or Hive) HW off
2. Hot water cylinder thermostat satisfied
You can see in the diagram below how wires from both of these two places connect to the motorised valves' grey wire. By doing so if HW is 'off' at the programmer or the hot water cylinder thermostat grey is made live.
It would be real coincidence if the tank thermostat was faulty at the same time as swapping the hive unit. So I wonder if the hive unit is actually providing the HW off mains supply? I could try and measure this at the control box?? A faultly Hive unit would make the most sense?
The easiest way would be to check for 240v on Hive terminal 1 with the HW set to off. Remove the wire that is currently in the terminal for the duration of the test to prevent any unwanted voltage coming from it.
Yes, so I would check the Hive first, but it may be possible for you to have disturbed the wire from the cylinder thermostat or the Hive in the wiring centre when you were inserting the link for the room thermostat.
However, when the Hive is set to HW off the grey should be live regardless of the position of the cylinder thermostat, and from your 'truth table' it's not.