Bonding
4 Oct 2012
East Renfrewshire
All - I know that this has probably been done to death but given there doesn't seem to be a real consensus on the subject, depending on who you talk to and given changes in the latest regs and nothing recent on the forum.
As a plumber/gas engineer we are taught as part of the C&G tech certs that bonding (equipotential and supplementary) is required when installing metal pipework and fittings in a home, especially on Gas pipework and any other associated metal pipework/fittings even when RCD's are present and given a lot of external supply pipework is now transitioning to plastic so there's no natural path to ground any more. I think it is also referenced in BS 7671 as a specific requirement for metal work and that then links to Part P using that standard to define a system as being safe.
What is the bottom line, is it needed as a standard and part of the regs?
TIA
As a plumber, are you recertifying your electrical competence part of your training on a regular basis like the electricians are?
AUIU the rules change pretty often as new things come to light and changes to what they do are required.
From what I see there are regular courses required by electricians to keep up to date with all this.
Which is why the recommendations on bonding changed.
All bonding is equipotential, that's the whole point of it.
Equi = equal
Potential = voltage.
Keeps two or more conductive parts at the same voltage by connecting them together.
When faults occur within an electrical installation, the main earth terminal and everything connected to it will have a higher voltage until the fault is cleared by the circuit breaker opening.
No bonding installed = metal items which are part of the electrical installation could have a higher voltage than other metal items entering from outside.
This could mean that when a fault occurs the metal case of a toaster has a higher voltage than the kitchen tap connected to metal pipes which enter from underground.
Someone touches both at the same time, they get a shock.
With bonding installed, both parts are kept at the same or very similar voltage = no shock.
Main bonding - connecting conductive parts which can bring a potential / voltage into the building to the main earth terminal.
Typically metal gas / water pipes which enter from underground, and bring Earth potential into the building.
As water and gas supply pipes have been plastic for decades, main bonding is less relevant than it was.
Supplementary bonding - the same principle applied to one location, such as a bathroom.
Relevant when all internal pipework was copper or steel, and most electrical items had exposed metal cases. Mostly irrelevant now due to the massive prevalence of plastic pipes and plastic lights, switches, and everything else.
Then there are all the things which were bonded long ago but never needed to be. Radiators, metal baths, boilers, kitchen sinks, metal window frames and the rest. None of those things could bring any potential into the building and yet a whole pile of dodgy 'guidance' was shovelled out by the usual suspects mostly in the 1970s/1980s implying that unless grotty little green and yellow wires were strung between every metal item in the building, instant death would occur.
Bonding is needed where it is needed.
It's not a 'shove this in and all is well' - every installation has to be assessed individually.
There are basic requirements and content, as part of the C&G tech training that cover electrical safety and bonding is part of that. Once completed that part of the course then there is no requirement to return to update, if and when any subsequent requirements may change. So no, we don't need to
So as part of 'due diligence' I guess, it's always good to keep up to date with anything that may influence specific decision as part of daily work or how to direct clients on a day to day basis. The default though is always to direct the client to the relevant professional for advise.
The requirements for bonding can seem to 'change' though depending on the electrician asked.
I also find the question of bonding hard to answer, even as an electrician.
So if I have a bit of class II electrical equipment used outside so not within the equipotential zone, and no problem touching the ground and the equipment at the same time.
But with an outside socket I have to connect the earth, so if using class I equipment then the soil and the equipment can be at a different potential. So we are not permitted to connect caravans to a TN-C-S supply, and EV chargers need loss of PEN protection.
In the house there is less of a problem as we are within an equipotential zone, it is where something moves between outside to inside not so bad with water, it can likely carry 100 amps through the pipe, the problem is mainly with gas pipes which, if they are asked to carry 100 amp, they could melt, so just as important not to include some items going outside as it is to include items inside.
So a water supply, and gas supply brought to the home in plastic, with just a short lenght of metal pipe as it enters the house there is not a problem, the other way is to have some insulating block.
But within the home, as long as all metal comming in to the home have been bonded to the electrical earth point, short lenghts of metal used where seen to look better, don't really need bonding.
The old idea was, if a dog was to knock over a standard lamp, in the room your in, you will see it, so even if the bulbs element is resting on the radiator, you will see there is a problem. But if in another room, then you could touch a live radiator as you have no idea what the dog has done.
We went mad on equipotential zone bonding, metal window frames, even door handles, then it was realised if you touch a radiator at 230 volt above true ground, as long as everything else is also at 230 volt, it is like a bird on the power lines, and there is no problem.
The main problem is entering and leaving the building, so as long as around the door nothing is bonded to either the true ground or the PEN, you will not get a shock.
Which leaves things like mobile homes, caravans, boats, porta-cabines, metal garden sheds, and garages etc. So these are not permitted to have a TN-C-S supply.
But this also leaves a problem, if a water pipe is metal and is connected to the PEN, and you put an earth rod in near to it, then that earth rod maybe at the PEN polarity rather than true earth.
I can continue for pages, only safe way, is ban TN-C-S, can't see that happening.
However, short lengths of pipe don't in general need bonding, and we hope that the RCD will pick up and trip when bonding is poor.
But I am stopping, as to list all is near impossible.
Bonding is needed where it is needed. It's not a 'shove this in and all is well' - every installation has to be assessed individually.
Very good summary.
The one thing you don't seem to mention (but obviously will know) in your concluding statement (quoted above) is that not only is bonding not needed when it's not needed but, worse, if things are bonded that didn't need to be bonded that can, in some situations to lead to an increased risk of electrical shock - not because it is 'bonding' but because it also 'earths' things - and unnecessarily creating extra earthed metal for people to touch (at the same time as touching something 'live') can increase the risk of electric shocks.
I guess the "it all depends upon the electrician you ask" is based on how recently they did any learning.
An old electrician might not know the current regs and recommendations as well as a new one.
I guess the "it all depends upon the electrician you ask" is based on how recently they did any learning. An old electrician might not know the current regs and recommendations as well as a new one.
Yes, I'm sure that there's some truth in that. In particular, the youngsters will presumably never have beeb exposed to the 'bonding mania' of the past (although they will still be seeing some evidence of it).
However, as I've said, I'm sure that the regs also have a lot to answer for. They' have (in my opinion) never been as clear about bonding as they could/should have been and I think that it was primarily poor wording of regs that led to the widespread misinterpretation of the regs which caused a lot of the 'bonding mania' in the past. Indeed, there are still some very confusing aspects of what the regs say about bonding, which some people probably regard as 'incorrect'.
As I often discussed her with the (sadly, increasingly probably 'late lamented') EFLI, the tests they describe of the need for/adequacy of supplementary bonding seem, to me, to be just plain wrong (well, no-one, not even EFLI, have challenged my view to date) :-)
I think you’re saying that you believe gas and water underground supply pipes being plastic means that bonding is now more necessary than before when they were metal, right? If so - no, that’s exactly the wrong way around.
I would like to think that maybe someone has created a nice simple document, with some diagrams, and maybe a flowchart, to help people including plumbers work out where bonding / supplementary bonding / etc. is needed. I haven’t found one, and everything from the IET looks like it’s deliberately hard to understand unless you’re already very familiar with their obtuse terminology.
Personally, I’ve found plenty of unnecessary earth wires and also missing required bonding in the places that I’ve lived. It’s a widespread problem.
Indeed so. He's posted much the same in the plumbing forum, and earlier this evening I responded to the same point (in that forum) with (as well as a lot more!) ....
You're thinking seems back-to-front. It is because an increasing proportion of water/gas supply pipes are plastic that even 'main bonding' (of pipes entering building) is often not required these days. When the supply pipes are metal, thereby providing a 'permanent path to ground', that is a potential problem, not a 'benefit'!
Yes, I too would like to think that such a document would exist - but, as you say, it appears that none does. Part of the reason may be that, over the years, some of what BS7671 has said about bonding (particularly, but not exclusively, in relation to gas meters and gas pipework) has been so confused/confusing (or even perhaps 'wrong'!) that third parties may be hesitant to produce easily-understood guidance because they are not, themselves, certain that they understand what BS7671 is (or should be) actually 'requiring' ?
Same here. If there's a saving grace, it's that the need for bonding is reducing all the time, and will continue to do so. Even today, very little supplementary bonding is really needed and, as supply pipes continue to be changed to plastic, the need for even main bonding will progressively diminish. Future generations of tradespeople may not even know what bonding is (or 'was') :-)
There are also the gas meter installers who may decline to install a meter if bonding is not present, even though the incoming supply is plastic.
There is also the situation where a plastic gas supply pipe feeds a meter in an outside cabinet but copper pipe leaves the meter cabinet clipped to the outside wall for some distance before it enters the property. Does that copper pipe need bonding? Does it make a difference how high above ground level that copper pipe is? Does it make a difference if potentially wet vegetation is touching that outside copper gas pipe, or might in the future?
They should fit it and notify the customer to employ a competent person to check whether bonding is required. That's what they are taught.
I would have thought that it's basically daft for a gas meter installer to refuse to install a gas meter because bonding is not present, even if (electrically speaking) that bonding is required. Bonding exists solely to protect against electric shock (and even that only in very uncommon circumstances), and has got absolutely nothing to do with gas.
In fact, if one does bond a metal gas pipe (because it is required) then, under certain fault conditions that bonding could result in very high electrical currents lowing through the walls of the pipe, potentially resulting in very high pipe temperatures or even, in some circumstances, sparks. So, in that sense, things are at their 'safest' from the gas point-of-view when there is no bonding.
Anything might happen in the future, so there's a limit to how far one can sensibly take such thinking - for example, a pipe two feet (or more) above ground level could one day find itself 'underwater' if there were severe flooding!! What is needed is common sense. Wet vegetation would virtually never be a problem. All common sense really requires is that one ensures that any metal pipe in electrical continuity with the pipe that enters the property is sufficiently high above ground level that is is extremely unlikely that it will ever be submerged in water that is sitting on the soil.
As I've just written, if bonding is required that is for electrical reasons and absolutely nothing to do with gas.
As I've also mentioned the only real relevance of bonding to 'gas issues' is that the gas situation is theoretically 'safer' when therein no bonding (since I doubt that gas folk would be totally happy with {admittedly fairly improbable} red hot gas pipes or sparks at joints in gas pipes :-) )