RCD tripping issue (again) - Earth Leakage?
Here are a few photos. I would have taken more but it has started to rain heavily...
Note: I've numbered the junction boxes on the original plan.
J3 on C1 is where the two new light fittings were attached. The photo shows their positions and how they are currently NOT connected within the junction box:
The following is J2 on C1, so this is the junction box prior to J3 i.e. there's a SWA between J2 and J3. J2 has a light fitting (the same make) as the 2 new ones:
And here's J1 on C1. No fittings currently connected to this:
Obviously, the above is only 1 of the 6 garden circuits. Once the rain stops I'll try to get some photos of the main garden junction box.
A photo of the main garden wiring box as installed by the electrician. Note, all the SWA earths are connected OUTSIDE the box using earth tags and he has then drilled through the box to fit the screws and earth cables inside. Not sure why he did it this way, rather than fitting the earth tags on the inside of the box, or even better, using piranha nuts:
One for the electricians.
Mate had tripping box on final day of rewire when outside lights were fitted.
Disconnected lights and all good. Reconnected and all good for a bit then tripped.
Wired outside lights to neighbours outside socket and all good.
Wired back in fusebox and tripped it.
Eventually sparks took fusebox off wall and tested and no fault found.
Gave a smack and a small bit of wire fell out.
That was doing it!
Wasted hours trying to understand what the fault was.
Off the top of my head don’t make a lot of sense
Which connection box did you alter?
J3 on C1. I added the two new lights to this junction box. The photo of J3 above shows them currently unconnected, so essentially only the SWA is "connected" (SWA earth wire and SWA steel wire).
Regardless of the two new light fittings being connected or not connected, the RCD still trips., but it was the connection of these two new light fittings that seems to have started the RCD tripping. I had assumed that removing them would removing the tripping issue, but that didn't happen and so far nothing I have removed has resolved the issue.
Wiring gets to be a head scratcher when you have all different colours sleeved as N and E like that
I did consider purchasing the following from Toolstation: Earth Leakage Clampmeter
Which would allow me to measure the earth leakage from all the circuits in the consumer unit and also each of the garden circuits connected to the garden wiring box.
While useful information, I'm not really sure what I would do with that information, since it is likely I would need to get an electrician to resolve the issue and I would expect them to have this equipment. If I also go ahead with the consumer unit upgrade, that is likely to be a big cost and again, I would expect the electrician to resolve any earth leakage issue that might cause tripping as part of that upgrade.
OK, I will start with a guess. My guess is the 2019 electrician got it working by not connecting an earth wire, which when you came to work on it, you have re-connected it as it should have been.
However, we have three tools, the insulation tester, VC60B.jpgthe RCD tester, RCD tester ramp.jpg and the clamp-on ammeter, Diffrence line neutral 8 Feb 24 reduced.jpg while it is tripping the latter two do not help, the insulation tester is the main tool. The problem is none of them are perfect. The insulation tester uses DC, so it does not test for inductive or capacitive linking, but this is unlikely to be a problem, so the RCD or RCBO (the latter is a RCD and MCB combined) at 30 mA has three limits. 1) Must trip at 30 mA. 2) Must not trip at 15 mA. 3) should not have background leakage over 30% so 9 mA.
In real terms often they will hold until around 27 mA.
So ohms law and maths, 230 volts / 0.009 amps = 25KΩ, so the reading must be better than that, and we consider it should be better than 1MΩ so that's only 0.23 mA.
So google and this 1786983051270.pngseems to be about the cheapest and is likely cheaper than hiring, as every time hired they need re-calabrating but your not really interested in super high accuracy.
So what you have to decide, is it worth learning how to use one, or is it simplier to get an electrician to do it all for you. The clamp-on is around £35 but you can do without it, and the RCD tester around £100, but again often we can get away without it.
As to any other way, well some RCDs X-pole.jpg do give a warning before they trip, and splitting the circuits over a number of RCBOs can also help, but you seem to have a fault, which still needs finding. And you have already tried the disconnect method of fault-finding.
To test, the neutral needs to be disconnected from the earth, and the supply connects neutral to earth, so it needs a double pole disconnection. So when in the house, always unplug rather than switch off, as that disconnects the neutral as well as the line (both line and neutral are called lives).
One of the hardest faults to find is the neutral to earth fault, as it often depends on the load, as to if it causes the trip, so a bit of wet toast in a toaster switched off but plugged in, can cause a trip when the kettle is switched on.
So step one is unplug all you can, seems unlikely I know, but the fault may not be in the garden, so anything supplied by that RCD, unplug if you can't unplug then OK switch off, as some switched are double pole.
Since moving into this house, I have had three times when the RCBO has tripped, one was a clear fault, the roof leaked into a socket, the other two, in spite of having the test equipment shown, they disappeared without my finding the fault, likely some interferance suppressor went faulty and the testing with 500 volt clearly the fault. Or I fried a spider or fly while testing, but I thought I had found the fault, but then the dish washer showed clear, and all plugged back in and no trips, and the clamp-on showed I was no where near the limit.
The tester does use 500 volt or 250 volt DC to test, if we think something may be damaged with 500 volt, or we have a surge protection device (SPD) fitted we use 250 volt, but normally we use 500 volt. So it is a case of keeping fingers clear, on the odd time I have been tested, when a forman sent two of us on the same fault and we were unaware of each other, on a locked off system I did get a belt, it was a good job the foreman could run faster than me.
But you need to be aware of what you are working with and what you are doing. And never work alone, if something does go wrong, you need someone to call emergency services.
It is easy for me to say DIY, I do know what I am doing, but that means it is hard for me to know how others would work with my test gear, I have worked with it all my life.
Wiring gets to be a head scratcher when you have all different colours sleeved like that
It definitely doesn't help, but I haven't changed anything in the wiring box apart from disconnecting and reconnecting the various circuits during testing, and I've checked all the wires to ensure neutral, live and earth are only connected to each other.
I confess, I would much rather use something other than those plastic terminal strips, more like a wago connector. It does seem very messy inside that box.
The thing that does stand out is the lack of consistency of use of the grey and black as the CPC so I would say proper continuity tests are essential
I can’t follow these threads too old :giggle:
A wiring mixup usually means an instant trip at switch-on or at power-up.
Was that confirmed here ?
However, we have three tools, the insulation tester, View attachment 420605the RCD tester, View attachment 420606 and the clamp-on ammeter, View attachment 420607 while it is tripping the latter two do not help, the insulation tester is the main tool. The problem is none of them are perfect. The insulation tester uses DC, so it does not test for inductive or capacitive linking, but this is unlikely to be a problem, so the RCD or RCBO (the latter is a RCD and MCB combined) at 30 mA has three limits. 1) Must trip at 30 mA. 2) Must not trip at 15 mA. 3) should not have background leakage over 30% so 9 mA.
So google and this View attachment 420609seems to be about the cheapest and is likely cheaper than hiring, as every time hired they need re-calabrating but your not really interested in super high accuracy.
As to any other way, well some RCDs View attachment 420614 do give a warning before they trip, and splitting the circuits over a number of RCBOs can also help, but you seem to have a fault, which still needs finding. And you have already tried the disconnect method of fault-finding.
Thanks for that helpful information.
I did read about the resistance tester, but putting 500V through the house wiring is not something I would want to do as I'm almost sure I will damage something and then I'm in a worse situation!
I did wonder if an earth leakage clamp would help identify if the cause was due to a combination of circuits and this tool seems to be very easy to use. However, assuming I did identify some earth leakage on circuits other than the garden, I'm not really in a position to start fixing these, so would probably then end up getting an electrician, meaning the cost of the earth leakage clamp, while an interesting exercise, probably won't get me anywhere and is just throwing money at the issue.
I do like the idea of all the existing MCB's being replaced by RCBO's, which should then isolate the tripping fault to the garden, assuming that circuit is the main issue.
I can’t follow these thread too old :giggle:
A wiring mixup means an instant trip at switch-on . Was that confirmed here ?
I don't believe it is a wiring issue, since the garden lights do not always trip instantly they are turned on. I've also been unable to identify any particular one of the 6 garden circuits (1 MCB in the junction box, but 6 separate cables from the garden wiring box) as being an issue, since eventually, regardless of which ones are connected to the garden wiring box, the RCD will trip.