Quick question...
In the garden there is an outdoor socket. From that 2.5mm SWA to an outside fused spur. From the spur 1.5mm SWA to a junction box that powers a couple of outside lights. The junction box is next to a greenhouse. I want to install a socket in the greenhouse to power 2 x 17.5w heated germination pad, no other devices. The junction box is about 20m from the spur.
Would 1.5mm SWA from the junction box 2m away to a new socket be too small? As its coming from a 13amp spur, I think it should be ok. Can someone please confirm if I'm right? It would save me having to run 20m of 2.5mm SWA to the greenhouse.
Thanks.
In the garden there is an outdoor socket. From that 2.5mm SWA to an outside fused spur. From the spur 1.5mm SWA to a junction box that powers a couple of outside lights. The junction box is next to a greenhouse. I want to install a socket in the greenhouse to power 2 x 17.5w heated germination pad, no other devices. The junction box is about 20m from the spur.