16 mm2 swa feeding 20A adistance of 125 M is this distance too great. The swa is buried in the earth.
 
Sponsored Links
chowbasa said:
16 mm2 swa feeding 20A adistance of 125 M is this distance too great. The swa is buried in the earth.


Nope, the volt drop over that distance for that load is 7V so well within the 4% (9.2V) limit imposed by BS7671.

However will whatever it is powering have a heavy startup current?
 
Sponsored Links
chowbasa said:
No just vac cleaner & some lights.

So where does the 20A come from then??

When calculating cable size you should worry about the supply you NEED.

If you have a 2kW hoover...8.6A

12 of 100W lamps = 5.2A ( I know you won't have 12 lights..just an example)

Total load = 13.8A

Protect it with a 300mA 16A RCBO at the supply end, and two seperate circuits the other, one a 16A RCBO for the socket and a 6A MCB for the lights.

That being the case, the cable required would be 10mm2, thus saving a considerable amount of money on the cost of cable.

If you can drop the total load below 10A, then the cable required will drop to 6mm2 and still meet the regs.
 