2 months with CH issues

You might be able to balance the rads to give more heat to the colder ones.
Even though a 5.0M head should be more than adequate for any CH system you could change the pump to speed3 which gives a 6.4M head, then adjust the ABV to say setting 0.55ish, if the system is noisy (or no improvement) then revert to speed2 and ABV to 0.45.
 
Sponsored Links
You might be able to balance the rads to give more heat to the colder ones.
Even though a 5.0M head should be more than adequate for any CH system you could change the pump to speed3 which gives a 6.4M head, then adjust the ABV to say setting 0.55ish, if the system is noisy (or no improvement) then revert to speed2 and ABV to 0.45.
Thanks so much. I did this and it's been over a week now and the system is working perfectly. Even the last radiator which has never been a good behaver is toasty.

Altogether the advice on this forum has been exemplary and I'm so thankful to everyone
 