- Joined
- 11 Jan 2004
- Messages
- 46,888
- Reaction score
- 3,988
- Country
The On Site Guide advises that a Zs value in excess of 200 Ohms merits further investigation - does this apply to all systems?
securespark said:In practice, Adam, what in your experience is the average Ze on a TT system?
i presume the comment is aimed at TT systems as on a TN system you really shouldn't be having Zs anywhere near that high (its afaict considered bad practice to rely on rcds for earth fault disconnection on TN systems).securespark said:The On Site Guide advises that a Zs value in excess of 200 Ohms merits further investigation - does this apply to all systems?
There's always something you can do.Adam_151 said:I's most certainly say yes, with TT its because its likely to be unstable (though I've heard that in some places you can't do a damn thing about it because of the nature of the soil around the place)
james 29 said:the ze reading of a tt system should not be more than 100 ohms or it is deemed unstable. The value used to be 200 but an ammendment now requires 100 ohms. The niceic endorses the 100 ohm rule but ithink the IEE are still 200.