hi, TT system rod value 85 ohms, periodic test form has box for max Zs permitted by BS 7671, has box for R1 + R2, and has box for max measured Zs so far so good. however with all bonds connected Ze at board is 20 ohms max Zs for 6A b type breaker (used to be 8ohm now 7.67ohm). So reading on lighting is 21 ohms at furthest point so i`m putting max allowed in one box as 8 ohms or so, and max measured 21 ohms what are we supposed to put in? these two readings are contradicting each other, any help gratfully received