No, but an Internet forum can point him at information from which he can learn about voltage drop, cable de-rating factors, installation methods, the importance of R1+R2 etc etc....
I quite agree. Though that's a bit different from 'Can I or can't I?'.
BTW, for anyone interested, my reasoning on derating the MCBs went as follows.
433.1.5 requires the cable used in ring finals to be able to carry not less than 20A.
The closest reference method to the conduit would be Reference Method B.
The Current Carrying Capacity table which applies to flat cable is 4D5. This table does not specify Reference Method B values but does give figures for A and C. By examination, B is clearly a case somewhere between A and C, and therefore a single flat cable will have a capacity of between 20 and 27A.
At this point, for two cables, I should have applied the grouping factor in Table 4C1. For 2 cables this gives a factor of 0.8. Using this factor, the current carrying capacity of between 0.8 * 20A and 0.8 * 27A. i.e. between 16A and 21.6A. Most of that range lies below 20A, so it is extremely questionable whether 2 x 2.5mm cables in conduit comply.
I would be interested in any feedback on this, as I have a current interest in the problem. My instinct is probably not to worry about it in practice.
(In my original recollection I was using the grouping factor specified in 2.3.3.1, which gives the grouping factor as 1 over the square root of the number of cables. For 2 cables this gives 0.71.
That would give a capacity of between 14A and 19A, which clearly doesn't comply. However 2.3.3.1 is a 'play-it-safe' approach specifically for different size cables, so it is not necessary to use it here.)