4Kw electric double oven install

Discussion in 'Electrics UK' started by Littlefoot2, 21 Sep 2021.

  1. Littlefoot2

    Littlefoot2

    Joined:
    18 Oct 2016
    Messages:
    15
    Thanks Received:
    1
    Country:
    United Kingdom
    Hi all
    The missus has decided she wants the gas oven removed and replaced with a
    electric double oven. It is rated at 4Kw. From cooker to consumer unit it is 10 metres.
    I have looked in the forum and have seen 2.5 mm cable on a radial circuit would be ok or 6mm
    cable.
    I have some spare 10mm cable can I use this instead? I know its a bit overkill but it will save buying more cable and it would help me for future upgrades, ie, electric hob.
    I have a spur 40mA MCB in the CU could I use this or would I have to replace with a 32mA MCB.
    The cable would be run under floorboards and rest on the concrete footings.

    Thanks
     
  2. Sponsored Links
  3. flameport

    flameport

    Joined:
    10 Mar 2007
    Messages:
    9,920
    Thanks Received:
    1,988
    Location:
    Poole, Dorset
    Country:
    United Kingdom
    Larger cable can be used, the only minor issue is that it will be more difficult to connect into the terminals of certain accessories.
    10mm² cable can be used for a 40A circuit provided the cable isn't run through insulation or installed in certain other undesirable ways.
    New circuits are notifiable work in England and Wales.
     
  4. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,455
    Thanks Received:
    4,199
    Location:
    Retired to:
    Country:
    Portugal
    6mm² cable can be used for a 40A circuit provided the cable isn't run through insulation or installed in certain other undesirable ways.
     
  5. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,455
    Thanks Received:
    4,199
    Location:
    Retired to:
    Country:
    Portugal
    4kW @ 240V is 17A so you could use 1.5mm² cable and 20A MCB
     
  6. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,186
    Thanks Received:
    555
    Location:
    London
    Country:
    United Kingdom
    Check those again. 40mA will just about supply a 100 watt bulb, no more.
     
  7. Littlefoot2

    Littlefoot2

    Joined:
    18 Oct 2016
    Messages:
    15
    Thanks Received:
    1
    Country:
    United Kingdom
    Sorry typo error. The mcb is rated at 40A.
    I can get some 2.5 T&E to run on a 32a MCB, but for future upgrade I will most
    probably go with the 6mm and 32mA MCB.
    As Flameport pointed out the cable would be difficult to connect to fixtures.

    Thanks Guys
     
  8. davelx

    davelx

    Joined:
    26 Sep 2006
    Messages:
    1,927
    Thanks Received:
    171
    Location:
    London
    Country:
    United Kingdom
    2.5mm² T&E is rated 27A at best, so you can't use that for a radial circuit on a 32A MCB.
     
  9. denso13

    denso13

    Joined:
    22 Jan 2007
    Messages:
    5,638
    Thanks Received:
    1,117
    Country:
    United Kingdom
    Don't worry, 99.9% of people new exactly what you meant.
     
    • Like Like x 3
  10. Sponsored Links
  11. BS3036

    BS3036

    Joined:
    24 Sep 2007
    Messages:
    944
    Thanks Received:
    68
    Country:
    United Kingdom
    It's just the odd 0.1% who didn't.
     
  12. SUNRAY

    SUNRAY

    Joined:
    28 Jul 2009
    Messages:
    5,574
    Thanks Received:
    427
    Location:
    Kent
    Country:
    United Kingdom
    So that will be 1 in a 1000 who didn't understand. I dare say that persons name began with 'w' and the '1' (in the 1000) came at the end.

    Now we know what the '1' is for:ROFLMAO::LOL:
     
  13. wundaboy

    wundaboy

    Joined:
    27 Apr 2008
    Messages:
    135
    Thanks Received:
    16
    Location:
    Shropshire
    Country:
    United Kingdom
    2.5 on a 20a MCB would do fine.
     
  14. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,455
    Thanks Received:
    4,199
    Location:
    Retired to:
    Country:
    Portugal
    Do you not already have a 'cooker' circuit?

    If not just install the standard cooker circuit of 32A and 6mm² (4mm² would probably do) from CU to cooker switch to dual cooker outlet near the oven. Use 2.5mm² from outlet to oven.

    Then you can just add a hob whenever you want.
     
  15. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,186
    Thanks Received:
    555
    Location:
    London
    Country:
    United Kingdom
    I think everyone knew what he meant. But it was wrong and needed correcting.
     
  16. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,544
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
  17. TimboTwo

    TimboTwo

    Joined:
    30 Jan 2021
    Messages:
    156
    Thanks Received:
    28
    Country:
    United Kingdom
    Pedant!
     
Loading...

Share This Page