And where do we stand on the fact that the 1.5mm flex is only 1 meter long, in free air. Does that still mean it needs a 16A MCB John?
Also consider that the conductors are doubled up in this case. (only at one end though). 1 driving 2 'hot plates' and 1 driving the other pair.
Yes, if you get a short you need protection, but the benefit of having pairs of live conductors is lost if you stick ONE 16A MCB for both live conductors. (2 16A MCB's would be fine - Then it would be like europe)
In this rare instance the manufactures are happy with it, and we are not, they must have satisfied themselves its ok!
(unlike fan manufactures requesting a 3A fuse etc.)
Also note, these electronic induction hobs, automatically limit their current to 32A, (in fact in the 'settings menu', you can probably limit them to 16A and 10A - NEFF) so it's only under failure conditions.
e.g a short on one cable, or one of 4 triacs? shorted, turning on one 'plate'
Also consider that the conductors are doubled up in this case. (only at one end though). 1 driving 2 'hot plates' and 1 driving the other pair.
Yes, if you get a short you need protection, but the benefit of having pairs of live conductors is lost if you stick ONE 16A MCB for both live conductors. (2 16A MCB's would be fine - Then it would be like europe)
In this rare instance the manufactures are happy with it, and we are not, they must have satisfied themselves its ok!
(unlike fan manufactures requesting a 3A fuse etc.)
Also note, these electronic induction hobs, automatically limit their current to 32A, (in fact in the 'settings menu', you can probably limit them to 16A and 10A - NEFF) so it's only under failure conditions.
e.g a short on one cable, or one of 4 triacs? shorted, turning on one 'plate'