dear bigburner,
you have been most helpful.
am i correct in thinking that i could do exactly as you suggested in terms of zoning/control (actually get a qualified person to do) while keeping the existing boiler ? the exisitng pump is a Grundfos UPE 40-80 F 250.
many thanks
VSR
The existing boiler will not have integral weather compensation. It can be added externally, but becomes more commercial then. I am trying to keep all domestic, so it is cheaper and easy for a domestic heating man to understand.
Depends on how the system is configured right now. Does it have two zone valves, one for CH and one for DHW? But, I would be inclined to do.......
The existing boiler can have a 3-way 28mm "diverter" valve [u[with an end switch[/u] on the boiler flow, switched via a cylinder stat. Grundfos Alpha smart pump between boiler and 3-way valve. A flow switch immediately after the pump wired into the room stat circuit of the boiler (switch out the burner only). Thermo rad valves on all rads. Have 4 zone valves one to each CH zone on the CH port of the 3-way valve. A cheap single channel timer controlling each zone, either on each floor or in a bank in a convenient place in the house. One timer for DHW too. No room stats, as the flow switch replaces that.
When running on CH: The 3-way valve is open to CH de-energised. If only one zone is switched on, or all zones, the boiler and pump run. If all TRVs close and no flow through the boiler, the smart pump backs off (modulates down) and burner is switch out via the flow switch. If the cylinder stat call for heat, 3-way valve is energises and sends all heat to the cylinder, by operating the pump and boiler burner. As there are no rad valve in the DHW circuit the pump winds up and switches in the flow switch and brings in the burner.
Have a tee before and after the flow switch and a 15mm in-line isolator between the level of the flow can be adjusted. before cut in and cut out.
You will then have a DHW priority system that sends all heat to the cylinder for a rapid re-heat, ensuring you rarely run out of DHW.