Surely switches only have to be rated to what they are switching, not to the CPD? This is why you can have 1.0mm² drops for switches on a 1.5 circuit as they are only carrying a relatively small current compared to the loop.
You could have 6A switches on a 10A circuit, no? After all, you have 13A accessories on a 32A circuit. Isn't that the same?
If you have a situation where something doesn't have upstream overload protection (because it can't overload due to chareristics) then you have to stop automatically assuming the CPD can provide protection against fault current and instead actually check it can... you do the adiabatic for cables, I expect you look at the spec sheet for accessories
As to the sockets, its part of BS1363 AFAIK that they are suitable for putting on 32A circuit, FCUS are BS1363 as well, 20A DP switches are not, so if you ever put ring conductors in supply and take a spur to a single socket from load, then it gets dodgy, its like a 20A jb on the ring circuit (unless the manufacturer tells you that the terminals are ok for that)... and as you'd use a 30A JB, you shouldn't use the terminals on the 20A DP either...
Not a lot I'd reckon, but you ought to check with the people whose accessories you are installing, rather than saying they look the same and its good enough (although I suspect in reality you could get away with excerising engineering jusgement like that and be perfectly fine unless it was a big project and someone went through it carefully)
Our good friend BAS, I believe Emailed MK on the matter and receieved some woolly non-commital answer, FWIW
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local