Is this right?
Not quite.
Total area of floor supported is 4.55m2, so with a floor live and dead loading of 2.15 kN per m2, that's 9.7 kN total load , and not 9.7 kN per m2.
But, you should use the effective span and not the actual span.
Either interpolate the effective span from the table, or just use the 1.5m span 1.58m effective span figures which will give a slightly higher load.
So work the area out again based on the above and then .. Divide total load by effective span to give a UDL in kN/m - which should be less than in that lintel table.