The blasé attitude to mixing different voltage bands in the same duct was not useful.
Why is it, I wonder, that it is considered safe for a person to touch the outside of an insulated and sheathed cable carrying 230V (maybe whilst in contact with something 'earthed'), but that there is perceived to be a potential (safety?) problem if it comes in contact with another insulated and sheathed cable (which may not be specced as 'insulated to 230V') connected to ELV circuits?If so then the cable manufacturers' specs will say.
I don't find that argument at all convincing.Maybe because any faults or breakdowns will only affect the poor sod touching the cable, whereas an ELV circuit becoming 230V could cause much worse mayhem.
Maybe because any faults or breakdowns will only affect the poor sod touching the cable, whereas an ELV circuit becoming 230V could cause much worse mayhem
I don't find that argument at all convincing.
By what mechanism?Engineer at a transmitter site. Transmitter has failed. 230 volts on both legs of the incoming private wire from the control room.
By what mechanism?
The latter would presumably be irrelevant to this discussion.Either a cable duct fire or a damaged amplifier cabinet, can't recall which was the cause of that incident
so I still don't really understand the thinking behind the regulation.
As for a cable duct fire
You have rather moved the goalposts - that's three layers of non-conductive barriers between the two conductors than we have been talking about (with two insulated+sheathed cables). Having said that, I think the chances of their being any problem would be extremely small.Would you intentionally allow bell wire to come into contact with bare metal carrying 230 volts AC ?
What is this "paper-insulated ELV cable"?Without a catch all regulation about the separation of LV and ELV cabling it would be considered by some non thinkers as "acceptable" for paper insulated ELV cables to be in close proximity / contact with exposed metal 230 volts terminals. So far safe but then not safe if the atmosphere is humid and the paper insultation is damp.
Yes, I understand that, but my point remains - the regulation requires 'separation' of LV and ELV cables only if the latter does not have insulation 'rated' for the LV voltage concerned. If the ELV cable does have such insulation, then the regulations allow the two cables to be in contact. Once the insulation had melted and carbonised, the fact that it was 'rated' for 230V is hardly relevant!It is on the aftermath of a cable duct / cable tunnel fire when insulation has melted / been carbonised and water / foam has filled the ducts that ELV comductors can be affected by 230 volts from damaged LV cables.
What is this "paper-insulated ELV cable"?