    I was working at a customer's house yesterday (doing plumbing not electrics) when the customer asked if I would look at their Triton shower that was playing up. A year after it's installation, it has started tripping the MCB, but with a loud bang too, not just a simple trip!

    Apparently, the electrician that fitted the shower replaced the old single ceramic fuse (which was actually a nail!!) with a 40A MCB, still retaining the old single fuse box itself (I noticed the on/off switch on the fuse box is blackened too). From here, a 10mm cable goes out of the wall, alongside the external wall (no conduit to protect it) and into the roof void, before going back directly into the shower itself. There is no isolating pull-cord switch in between the fusebox and the shower and there's no sign of water getting into the unit.

    I've been back today and the customer flicked the MCB back on and the shower started working again, however, within 5 minutes the MCB went "bang" again and it's back to square one - no shower.

    I can't understand why it would start tripping out a year after installation so I wondered if anyone here as any clues. It's a Triton Zante 9.5kW shower if it helps. She has mentioned that the shower occasionally goes really cold, then really hot, so could that be associated with the problem?

    Cheers
     
  2. Sponsored Links
  3. LoveRocket

    LoveRocket

    Joined:
    28 Jan 2010
    Messages:
    641
    Thanks Received:
    75
    Country:
    United Kingdom
    What goes BANG - that shower or the MCB?
     
  4. dirty harry

    dirty harry

    Joined:
    24 May 2007
    Messages:
    40
    Thanks Received:
    0
    Location:
    Leicestershire
    Country:
    United Kingdom
    The MCB.
     
  5. bongos

    bongos

    Joined:
    7 Jul 2007
    Messages:
    1,078
    Thanks Received:
    82
    Location:
    London
    Country:
    United Kingdom
    From your description it sounds like a fusebox with rewirable fuses so I'm guessing the shower is not on an RCD? Or does it have a separate RCD enclosure?

    I wonder if there was previously a problem here hence the nail in the fuse carrier? A high impedance short of some variety might cause the MCB to trip once the it had warmed up nicely...
     
  6. dirty harry

    dirty harry

    Joined:
    24 May 2007
    Messages:
    40
    Thanks Received:
    0
    Location:
    Leicestershire
    Country:
    United Kingdom
    It is an old, single "rewireable style" fuse box which has had a modern 40A MCB stuck in it! There is no RCD enclosure that I see of.

    I guess there may well have been a problem with the box, as you say the fact there used to be a nail in the fuse carrier could be a hint!

    Anyone else have any ideas? Would it be worth swapping the old fuse box for a modern shower consumer unit?
     
  7. dirty harry

    dirty harry

    Joined:
    24 May 2007
    Messages:
    40
    Thanks Received:
    0
    Location:
    Leicestershire
    Country:
    United Kingdom
    Has anyone got an suggestions at all? PLEASE!
     
  8. LoveRocket

    LoveRocket

    Joined:
    28 Jan 2010
    Messages:
    641
    Thanks Received:
    75
    Country:
    United Kingdom
    I think the shower is goosed, mate.

    Does the shower still flow water with no power? (Turn it on, then switch of the isolator or MCB and see if the water still flows)

    Have you got an insulation resistance tester? There could be a fault on the cable, but it's far more likely to be the shower.
     
  9. dirty harry

    dirty harry

    Joined:
    24 May 2007
    Messages:
    40
    Thanks Received:
    0
    Location:
    Leicestershire
    Country:
    United Kingdom
    Thanks for the tip, must admit I was beginning to suspect the shower and I think you may have confirmed it. Haven't checked to see if there's any flow without power but can do it tomorrow.

    Cheers.
     
  10. Sponsored Links
  11. bongos

    bongos

    Joined:
    7 Jul 2007
    Messages:
    1,078
    Thanks Received:
    82
    Location:
    London
    Country:
    United Kingdom
    It could be the shower, it could be the cable. Or something else maybe.

    What power is the shower rated at? Are you sure it's 10mm² cable?

    It would be less common to have a 10mm² cable on an older BS3036 fuse box (not unheard of though). I wonder how good the last spark was if he did work last year and didn't install an RCD, which would almost definitely be a requirement of the MI and probably required by the 17th edition depending on what level of "intallation" he was actually doing...
     
  12. dirty harry

    dirty harry

    Joined:
    24 May 2007
    Messages:
    40
    Thanks Received:
    0
    Location:
    Leicestershire
    Country:
    United Kingdom
    It's a 9.5kw shower and the cable is definitely 10mm. I have to question why the electrician that fitted it did not replace the older fuse box with a proper MCB/RCD shower consumer unit, which the product instructions clearly said he should have done to comply with the warranty. Anyway, that's all in the past so, starting with the cheapest option, I've suggested to the customer that they have the old fuse box replaced with a proper shower consumer unit and see if that cures the problem. If it doesn't, it'll be a new shower!
     
  13. bongos

    bongos

    Joined:
    7 Jul 2007
    Messages:
    1,078
    Thanks Received:
    82
    Location:
    London
    Country:
    United Kingdom
    While having a shower CU incorporating a RCD is definitely a good idea, I still think it's likely there must be a fault elsewhere, possibly with the cable.

    However, any spark installing a shower CU will test the cable as part of the work so at least it will show up if there is a problem.
     
  14. dirty harry

    dirty harry

    Joined:
    24 May 2007
    Messages:
    40
    Thanks Received:
    0
    Location:
    Leicestershire
    Country:
    United Kingdom
    True, but would it not be odd for the cable to start playing up after a trouble-free 12 months? Having looked closely it was obviously brand new when it was installed a year ago.
     
  15. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
  16. dirty harry

    dirty harry

    Joined:
    24 May 2007
    Messages:
    40
    Thanks Received:
    0
    Location:
    Leicestershire
    Country:
    United Kingdom
    Thanks for that, a useful bit of info - it's definitely a 10mm and I did see 10 stamped on the cable too.
     