Good morning guys and gals. Looking for abit of advice on the following domestic situation. Sorry its a bit long. I am a qualified sparks, but I'm in the industrial field, where as you can imagine MD is abit more straight forward!
Anyway the heads up is, I have been asked by a family friend if I would be willing to re-wire their kitchen. I'm not registered so this will be done under building regs notice when the time comes. So they want a new ring main put in, and a new 5.5kW double oven and a new 6.3kW hob (both seperate), where they had gas before. However my concern is the load that would put on the 100A main fuse. They have a split 2-RCD board feeding the following for a large 3 bedroom bungalow:
- Shower 40A
- Bedroom ring main 32A
- Lounge/Dining room/Hall ring maom 32A
- Kitchen Ring main 32A
- Boiler house feed 32A (Also feeds sockets for washing machine, tumble dryer)
- Attic socket and light 16A
- Bedroom Lights 6A
- Rest of house 6A
And a seperate RCBO feeding the garages rated at 32A.
Using diversity guidlines and my own adjustments I have come up with the following:
Shower = 40A
Bedroom ring/Lounge/dining ring = 12.8A (I think the two ring mains are for convenience if there is a fault rather than the load)
Kitchen Ring main = 12.8A
Boiler house feed = 32A
Attic socket/light = 10A
Bedroom Lights (Approx 300W) 1.3A
Rest of house (Approx 300W) 1.3A
Garage Feed (Couple of sockets and a light) 12.8A
Total = 123A
As you can see with the new hob and double oven the MD is going to be well over the 100A main fuse. Do you think my calcs are ok? Or a bit over estimated? So should installing the new oven and hob be a problem? There could be a solution that they are having a new combi boiler installed, so I could get them to run a thermostatic mixer shower, rather than an electric shower, thus 'freeing up' the 40A shower feed, is this the best route to go?
I look forward to any response,
Thanks Scottyboyiow
Anyway the heads up is, I have been asked by a family friend if I would be willing to re-wire their kitchen. I'm not registered so this will be done under building regs notice when the time comes. So they want a new ring main put in, and a new 5.5kW double oven and a new 6.3kW hob (both seperate), where they had gas before. However my concern is the load that would put on the 100A main fuse. They have a split 2-RCD board feeding the following for a large 3 bedroom bungalow:
- Shower 40A
- Bedroom ring main 32A
- Lounge/Dining room/Hall ring maom 32A
- Kitchen Ring main 32A
- Boiler house feed 32A (Also feeds sockets for washing machine, tumble dryer)
- Attic socket and light 16A
- Bedroom Lights 6A
- Rest of house 6A
And a seperate RCBO feeding the garages rated at 32A.
Using diversity guidlines and my own adjustments I have come up with the following:
Shower = 40A
Bedroom ring/Lounge/dining ring = 12.8A (I think the two ring mains are for convenience if there is a fault rather than the load)
Kitchen Ring main = 12.8A
Boiler house feed = 32A
Attic socket/light = 10A
Bedroom Lights (Approx 300W) 1.3A
Rest of house (Approx 300W) 1.3A
Garage Feed (Couple of sockets and a light) 12.8A
Total = 123A
As you can see with the new hob and double oven the MD is going to be well over the 100A main fuse. Do you think my calcs are ok? Or a bit over estimated? So should installing the new oven and hob be a problem? There could be a solution that they are having a new combi boiler installed, so I could get them to run a thermostatic mixer shower, rather than an electric shower, thus 'freeing up' the 40A shower feed, is this the best route to go?
I look forward to any response,
Thanks Scottyboyiow