And what difference will that make?Pretty sure it's a combi

And what difference will that make?Pretty sure it's a combi

It can't call for heating and hot waterAnd what difference will that make?
It can't call for heating and hot water

Thanks for the detailed response, that's interesting. I remember hearing they didn't use a diverter valve but didn't put much thought into how that worked.I never said it could. But.....
The Intergas boiler uses a bithermic heat exchanger meaning it has two sets of pipework, one for the dhw and one for the heating.
With the setup the OP has when there is a call for heating it will go to the boiler and UFH pump. If the boiler is having a call for hot water at the same time it will ignore the heating demand.
However the UFH pump on the manifold will still run and it will create a parasitic flow across the boilers flow and return which will scavenge heat from the larger heating coil in the hex and cause poor hot water performance.
I was the senior engineer for Intergas in the UK for 5 years and have seen it happen many times but I will let you off as you weren't aware of this particular boilers unique properties. A more conventional combi would not have this issue.
BTW Just to make the OP re-evaluate how complicated he thinks his system is. This one I installed serves 250 square metres of UFH and 22 rads with priority domestic hot water, weather comp and Opentherm...
You are massively overcomplicating things.
Run the UFH manifold directly from the boiler with no blending valve/pump on the manifold or outside sensor. If you want to zone each area just do it with actuators and ordinary room stats
Then set the boiler flow temp to 40 degrees and lock it so no one can accidentally alter it.
No advantage whatsoever to using OT or WC in this situation
Yeah, that is a pretty scary sight to me at the moment.... So the fact it is an Intergas, and not a Vaillant is critical: I asked them to go for Intergas (possibly rather than their preferred WB or Vaillant..) so he'll probably turn it back on me.. Anyway, the same question arises; should I get them to remove that pump and blend valve if possible? Can it not run at a low enough temperature without a blend valve? (I thought the idea was to run a condensing boiler as low as possible anyway). I don't want to cause him to throw a hissy and disappear for another few weeks. Is there such a thing as a basic schematic showing the ideal set-up with an Intergas combi, that I can give to him? Along with the reasons you've given me, it would help me push the point home.I never said it could. But.....
The Intergas boiler uses a bithermic heat exchanger meaning it has two sets of pipework, one for the dhw and one for the heating.
With the setup the OP has when there is a call for heating it will go to the boiler and UFH pump. If the boiler is having a call for hot water at the same time it will ignore the heating demand.
However the UFH pump on the manifold will still run and it will create a parasitic flow across the boilers flow and return which will scavenge heat from the larger heating coil in the hex and cause poor hot water performance.
I was the senior engineer for Intergas in the UK for 5 years and have seen it happen many times but I will let you off as you weren't aware of this particular boilers unique properties. A more conventional combi would not have this issue.
BTW Just to make the OP re-evaluate how complicated he thinks his system is. This one I installed serves 250 square metres of UFH and 22 rads with priority domestic hot water, weather comp and Opentherm...
View attachment 397724
I already said what needs doing in my first post.
Basically flow goes into top rail of manifold and return to the bottom and that's it you dont need anything else.
The boiler flow temperature can be locked so it won't go above 45 degrees (or whatever the flooring manufacturer specifies) and you save money and hassle