EFLI is less than 2 OHMS
These are the reverse of each other, is it greater or less, If less, then no problem, if greater, then may be a problem. To me, it would alert me to look at the line - neutral impedance, the line - earth is covered by the RCD, the line - neutral is not, a B40 MCB will in fullness of time trip at 40 amps, but that would take a long time, so as well as the thermal trip, it has a magnetic trip which is very fast, that with a B should trip at between 3 and 5 times the thermal setting, so 5 x 40 = 200 amps, so 230/200 = 1.15Ω add 5% for safety, and we have 1.09Ω maximum line - neutral impedance to ensure the trip will open in time.greater than 1.09 Ohms
But it is the line - neutral which is important to be below 1.09Ω as the line - earth is protected by the RCD, most testers display the line - neutral in amps, so 210 prospective short circuit amps or higher.
So with amps not below 210A, and with ohms not above 1.09Ω for the line - neutral but for line - earth with a 30 mA RCD it is 200Ω or below which is required. However, if at the consumer unit I was to measure 0.35Ω and at the shower I was to measure 3Ω it would flag up a fault. We can expect the line - neutral to be a little lower to the line - earth, as the neutral wire is thicker than the earth wire, but not by much, in the same way with a shower 4 meters from the consumer unit, would expect 0.38Ω. To get 1.09Ω with 10 mm² looking at around 100 meters or more. So even if within the limits, unexpected readings should trigger a red flag, as something wrong somewhere.
But 2Ω seems odd, if it was 1.99Ω, or 2.01Ω it would seem correct, but to measure bang on 2Ω seems odd. This