Wylex split load CU
2 split aircon units connected to RCD side. every time they are switched on they trip the 80a 30ma RCD.
what could be causing this?
both units were recently installed!
High inrush currents on Aircon fan unit at start up. Dont know why they were put on RCDside . In fact you usually have to stick em on a C type breaker to stop the breaker tripping on inital start up.