Ariston eurocombiA/23 MFFI

Joined
1 Oct 2009
Messages
5
Reaction score
2
Country
United Kingdom
Hello, has anyone come across this fault,hot water works fine, heating gets to 40 deg on the display lights and shuts down,cools and repeats process.

The diverter valve has been checked, the water quality is good, the sensor has been replaced, the boiler will stay on with a spare sensor detached from the boiler, all the radiators will heat up nice and quick.

It sounds like the PCB but at £160 I thought I would check

Thanks in advance
 
Sponsored Links
It could be PCB (very expensive!) B4 going there, check the lead from the CH Thermister and the PCB for good connection and damage ;)
 
Sponsored Links
The control knob spindle on the central heating had worn out and was not turning up the aperture on the PCB, easy fix was swapping with the hot water spindle as this is always set to maximum.

Thanks for the replys
 