ASHP 22mm Pipe directly to std new radiator without stepping down to 15mm

It's a 4kw system with a water flow of usually around 12L/m. This flow reduces to 7.5L/m sometimes and as low as 5L/m on occasions.

The control unit says the temp difference between flow and return is about 5 degrees, it varies a little but no more than about 1/2 degree maybe a tad more on occasions.
You probably know this anyway from the display :
If the output is 4.0kW at 12LPM, then the dT is, 4.0*860/60/12, 4.78C, as reported by the control unit.
A flowrate of 7.5LPM (at a 5C dT) outputs, 7.5*60*5.0/860, 2.62kW
A flowrate of 5.0LPM (at a 5C dT) outputs, 5.0*60*5.0/860, 1.74kW
 
I'm confused - why would you have the heating on in the early hours of the morning?
It's cheaper to run by having an overnight setback of just a few degrees than having it controlled to to turn on and off at set times during the day.

Even over a weekend when i'm not at home it's cheaper to setback the temperature to 17 all day and night than have the heating off or controlled to turn on and off at preset times.

When the system was installed, the installer made it clear that the best way to use this ASHP system was to find a temperature i was happy with and leave it at that 24hrs a day. Explaining that it will be cheaper to run. The installer went on to say that if i set the system to turn on and off through the day it would take a long time to raise the temperature to the temperature i would want and it would cost more.

I have tried both approaches monitoring the performance and costs and they are correct. When turning off overnight the system takes hours to get back up to temperature and the same in the evening, it might get to temperature before i go to bed if i'm lucky!!!!!

However, leaving it on 24hrs it's getting far too warm for me in my bedroom, typically 21 degrees, sometimes as much as 24 degrees when its 19 in the living room. I want to turn this around in some way. I would be happier to turn the rad off altogether in my bedroom if i can find a way whilst at the same time increase the temp in the living room to 20/21. If i turn the room-stat up to 21 in the living room the bedroom temp gets to a very silly temperature!

When i try to gently restrict flow to upstairs rads (Reduce temperature upstairs) to move more water to the downstairs rads in the hope of pushing up the temperature a little (downstairs) i succeed to a point but not quite enough. If i push it too far the system switches off with water flow problems, flow too low. Noting when this happens i'm discovering that more often than not it's happening in the early hours and at the mo i'm assuming that it happens when the temperature drops to a point where the system turns itself back on again (or shortly afterwards after it's been running for a while) at a living room temp set at 17.

My gut feeling at the moment is to explore the idea of fitting a 2nd rad in the living room in the hope that i may be able to turn off the rad in my bedroom altogether or at least turn it down to a temperature that's ok (for me). 17/18 degrees!? The lower the better.

Now that the system is "Out Of Warranty" i feel that i can now do something myself without invalidating a warranty. The cost and process of fitting a 2nd rad in the living room is no big deal and if it doesn't workout i can either just turn it off or remove it.
 
You probably know this anyway from the display :
If the output is 4.0kW at 12LPM, then the dT is, 4.0*860/60/12, 4.78C, as reported by the control unit.
A flowrate of 7.5LPM (at a 5C dT) outputs, 7.5*60*5.0/860, 2.62kW
A flowrate of 5.0LPM (at a 5C dT) outputs, 5.0*60*5.0/860, 1.74kW
I didn't know this and i'll have a look at this and try to understand it and work out if it's somehow useful to me in some way. The info that the control unit gives me is limited and the level of control i have is limited too

Thank you
 