Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
If you can only get hot water with the heating on the most likely reason is the diaphragm in the water section is holded/worn.
The expansion vessel should contain air pressurised to about 0.7 Bar (with the system at zero pressure).
It is normal to have to drain a small amount of water out of the vessel on these older vaillant expansion vessels. These are high quality vessels and can easily give a service life of 20 years.
However more than a cupful may indicate a punctured vessel, in this case plumb in an additional vessel onto the system.
Yep wax stat diverter, Vaillant managed to get the design right where Potterton didin't.
I often find the screw holding on the water section is seized due to a leaking stuffing box. A small flame off the blowlamp sometimes shifts it otherwise down the breakers yard for a lower section.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local