Automatic By Pass Valve

Discussion in 'Plumbing and Central Heating' started by Sandy43, 13 May 2009.

  1. Sandy43

    Sandy43

    Joined:
    12 May 2009
    Messages:
    16
    Thanks Received:
    0
    Location:
    Berkshire
    Country:
    United Kingdom
    I have an Automatic By Pass valve model SBV22 by SUNVIC.
    I am trying to find a simple way to calibrate setting so that it opens when
    two ports valves in s-plan systems are shut (no heating or hot water)
    and minimum flow when any of the heating or hot water is on.

    The method described is quite complicated such as to set 20% above the
    normal pressure when working so this does not open premature.

    I find difficult how you would determine these setting figures.

    I saw an other Auto by pass in Srewfix and that comes already set at 2 bar and the setting can be varied.

    Is 2 bar a nominal value ?
     
  2. Sponsored Links
  3. Fluffster

    Fluffster

    Joined:
    5 Jul 2006
    Messages:
    1,242
    Thanks Received:
    42
    Location:
    London
    Country:
    United Kingdom
    Generally an open vented system will run around the .5 bar and a sealed system hot about 1.5 to 2 bar.

    Pete
     
  4. mogget

    mogget

    Joined:
    18 May 2008
    Messages:
    1,898
    Thanks Received:
    163
    Location:
    Wiltshire
    Country:
    United Kingdom
    I'm not sure how this would relate to a bypass valve, as your average 15-50 pump only produces a differential of 0.5 bar on maximum setting.

    I set mine using the unscientific method. First I set the bypass valve to maximum (ie, shut), and turned the boiler stat right down. Then I put the system onto pump overrun, and slowly turned the valve down until there was flow through it - the sound changes as flow begins. With the boiler stat back up you can check by feeling the pipes for heat.
     
  5. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,587
    Thanks Received:
    1,343
    Location:
    Kent
    Country:
    United Kingdom
    Allow heating to cool down
    Set ABV to max (7)
    Turn on heating with all TRVs and zone valves open.
    Adjust the ABV until you can just feel the pipe after the ABV getting warm.
    Turn the valve back slightly so it closes
     
  6. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    That's the easy way DH, and good enough in most domestics.

    Everything on full with the by-pass closed, then open the bypass slowly until you feel a flow through it, turn it back one full turn.

    Job sorted.
     
  7. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,587
    Thanks Received:
    1,343
    Location:
    Kent
    Country:
    United Kingdom
    The Sunvic is only one turn from open to closed!

    [​IMG]
     
  8. Sponsored Links
  9. doitall

    doitall

    Joined:
    8 Jan 2005
    Messages:
    19,003
    Thanks Received:
    1,538
    Location:
    Bath
    Country:
    United Kingdom
    Right, I've always used the AVDO
     
  10. Agile

    Agile

    Joined:
    26 Jun 2004
    Messages:
    64,017
    Thanks Received:
    4,591
    Location:
    London
    Country:
    United Kingdom
    I would recommend a better way to set it by closing all except TWO of the TRVs and then adjusting the ABV until it just starts to allow a small flow through it as evidenced by the outlet getting warm.

    Then leave it in that position!

    Turning back one turn is very hit and miss. Particularly if the valve only has one turn!

    Tony
     
  11. gas4you

    gas4you

    Joined:
    23 Feb 2007
    Messages:
    21,178
    Thanks Received:
    1,912
    Location:
    Norfolk
    Country:
    United Kingdom
    Honeywell's instructions are to close all rad valves, turn the ABV until it just starts to pass hot water, then turn back 1/2 a notch.

    I more often than not find it ends up set at about 3.5.
     
  12. D_Hailsham

    D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    10,587
    Thanks Received:
    1,343
    Location:
    Kent
    Country:
    United Kingdom
    Which is the only one where the instructions distinguish between a bypass used to maintain the minimum circulation through the boiler (left picture) and one used to limit the differential pressure across the radiator circuit (right picture).

     
  13. bengasman

    bengasman

    Joined:
    28 Jan 2005
    Messages:
    34,181
    Thanks Received:
    3,124
    Location:
    London
    Country:
    United Kingdom
    Your pumps are better than mine mate.
    The very best I can achieve under optimum circumstances is about 0.4 bar on a sealed system, which is the same as open vent by the way.

    Forget about all the numbers as they are not important.

    Easy way to go about is to turn the resistance to way more than needed.
    Stop the flow by closing all valves, or any other way you fancy, start the pump, slowly lower the resistance on your bypass until it opens. Now go about 0.2 below that.

    Repeat process at annual service to assure proper working is maintained.
     
  14. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page