Open the LS valve to reduce difference (raise return temp); close LS valve to increase difference (lower return temp).If the difference is, say, 20 degrees, should i be opening it to allow more flow and less of a difference?
similarly if the difference is only 5 degrees should i be closing it for less flow?
Not sure what you mean.i tried this this morning but the problem I've found is that the difference chnges between about 5 and 20 degrees so i'm not sure at what point to take the reading.
Only change one LS valve at a time, by a very small amount, i.e 1/12th turn or less, and wait 5 minutes for the system to settle down. If the boiler is cutting off and then restarting, you must wait until the flow temp is back up to 75C before checking the difference.
The reason for this is that what you are doing, indirectly, is setting the flow rate through the radiator and the same flow rate will produce a different temperature drop depending on the flow temperature. For example these all have the same flow rate, within a few %:
Flow temp: 75C; Return temp 65C. Difference 10C
Flow temp: 55C; Return temp 49C. Difference 6C
Flow temp: 45C; Return temp 41C. Difference 4C