• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Bathroom rads come on when either HW or CH is on

Joined
10 Dec 2010
Messages
3
Reaction score
0
Location
Buckinghamshire
Country
United Kingdom
Hi

Just brought a new build house and noticed that when either the hot water or central heating is on the bathroom rads come on, however if the HW is off they still come on when the CH is on.

The system is a Megaflow with TRV's fitted to all rads

I've spoken to the site manager as he reckons this is how its suppose to work.

Can somebody please advise how this works and if being heated by the HW circuit where does the flow return to as we fiited a water softener but were told not to use softened water to fill the CH system as it could damage the boiler.

Thanks
 
Nice to have dry towels in the summer months. :mrgreen: .........................................nothing wrong with this set up unless you talk to the green party :mrgreen: , the flow pipe to radiators is 'teed' off before any auxilary controls ie: motor valves , how this works is whenever there is a call for HW/heating the circulating pump will supply bathroom radiator with heat............the other reason could be the installers used the bathroom radiators as a bypass circuit/heat sink ('S' plan)
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top