hi guys,
the boiler fires up runs for about 20minutes from cold then lockout with 6 neons all red (not flashing) 23-28 in the manual.
I checked the expansion vessel while the system was depressurized with drain valve open and this was below the recommended 0.5bar and was repressurized to 0.5
the dhw works as it should on both dhw only and central heating and dhw
sometimes the central heating comes back on briefly after dhw is used but the flame (burner on indicator) then goes out with the fan and pump still running
there is a slight leak from the diverter valve grub screw but not sure which of the two diaphragm would cause this?
my plan is to firstly replace the central heating temperature sensor
secondly isolate /drain/empty boiler then check both diaphragms
if these two fail then the plate heat exchanger has a blockage or pcb faulty which i will have to get heating engineer in.
any advice will be appreciated
the boiler fires up runs for about 20minutes from cold then lockout with 6 neons all red (not flashing) 23-28 in the manual.
I checked the expansion vessel while the system was depressurized with drain valve open and this was below the recommended 0.5bar and was repressurized to 0.5
the dhw works as it should on both dhw only and central heating and dhw
sometimes the central heating comes back on briefly after dhw is used but the flame (burner on indicator) then goes out with the fan and pump still running
there is a slight leak from the diverter valve grub screw but not sure which of the two diaphragm would cause this?
my plan is to firstly replace the central heating temperature sensor
secondly isolate /drain/empty boiler then check both diaphragms
if these two fail then the plate heat exchanger has a blockage or pcb faulty which i will have to get heating engineer in.
any advice will be appreciated