Baxi 105e instant

Joined
10 Oct 2006
Messages
24
Reaction score
0
Location
Cumbria
Country
United Kingdom
Hi everyone when i put my ch on with only a 4 rads on the presure gauge goes from 1 bar to 2 bar wich i think is normal but if i put all 7 on the pressure gauge goes all the way round to 3 bar increasing a bit more with each rad that i put on. anyone any ideas ? it has just had a new expansion vessel put in to try and fix the problem but it is no different. The pressure in the vessel is 1 bar The boiler has been in for 18 months with no problems untill this
Thanks cris
 
Sponsored Links
Did you check the pressure in the new expansion vessel before you fitted it also did you check for blockages in the pipe connecting to the expansion vessel :confused:

an easy way to solve this problem would be to fit an external expansion vessel onto your heating pipework ;)
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top