I have an intermittant problem. The 80 fault light will flash and I have no water or CH. After a while the 80 light will go out and boiler starts up for water and CH but after 5 sec goes out and 80 goes on this repeats for a while then everything works fine. Fault usually starts when everything is cold. Any ideas?
 
The flashing 80 indicator means your primary ntc sensor is suspect..You can measure the resistance to confirm or if it is a chrome sensor then deffo change it...Part no 5108265
 
poxi said:
The flashing 80 indicator means your primary ntc sensor is suspect..You can measure the resistance to confirm or if it is a chrome sensor then deffo change it...Part no 5108265

Thanks - what should the resistance be?
 
300017 said:
Thanks - what should the resistance be?

11 ohms when cold

300017 said:
What are the 2 sensors - is one the primary NTC? and what is the other?
Thanks

Hot water

300017 said:
Thanks - what are the 2 sensors and where will I find them?

Follow the wiring diagram on the back of the boiler cover..Low voltage green and red wires go to them
 