I have a Baxi 105e Combi boiler, no hot water. No central heating either but that's not important right now.
Two faults displayed, Flame Failure and Fault on Fan or Flue.
I've been going through the DHW Fault diagnosis, can you tell me if I've missed anything please?
System pressure is okay at 1 bar
When opening the hot tap, DHW flow switch is activated.
Air pressure sensor at the main board is normally closed (as expected)
DHW temperature sensor is within normal range.
Safety overheat thermostat is normal - less then 1.5 ohms.
At the main board there is no mains voltage for the Pump or the Fan.
I'm thinking that the main board is faulty, I've checked the two identical relays on the main board by removing them to test and they're working as they should.
Thanks very much