BAXI 105e-Removed Radiator, Now no Hot Water and pump fail?

Joined
11 Oct 2006
Messages
44
Reaction score
0
Location
Nottingham
Country
United Kingdom
Hi there, my Combi Baxi 105e boiler has been working fine.

I removed a radiator today in prep for decorating.

Now i dont get any Hot Water from the Baxi and the Pump/Low pressure fail LED is flashing when a hot water tap in on...

Has anyone any ideas? Are the 2 related?

Cheers OP
 
Sponsored Links
manualy fill boiler to 1.5 bar via tap on flexi filling loop close to or under boiler.vent all rads downstairs first, returning to boiler as you are doing it ,continually topping the pressure up as you go.
 
Sponsored Links
Arr ok think i have filled it now. (one of the radiator valves wasn't closed so when i first tried it leaked water everwhere! doh)
 
Thank you very much for you help. All fixed now! Hot water again!

I ow you a beer or two.

Many thanks once again.
 