baxi 105e

Joined
28 Apr 2013
Messages
2
Reaction score
0
Location
London
Country
United Kingdom
hi i have baxime 105e, hotwater is coming on and off some time,heating is working ok ,pressure is ok, both swiches on valves are working ok,please help me thanks
 
Thanks a lot for your reply but please can u explain about blocked exchanger, you mentioned. What can I do for that. Thanks again
 
Thanks a lot for your reply but please can u explain about blocked exchanger, you mentioned. What can I do for that. Thanks again
the problem is that sludge has built up in the secondary heat exchanger, the small one that makes hot water. you should have a magnaclene fitted on the return pipe to the boiler. You will need to replace the secondary heat exchanger to cure the problem, and preferably get the system clean before you fit the new one.
 
No need to replace it as it takes less than 30 mins to remove and clean it
 
Plates are around 65 plus vat retail, might aswell try to clean it, ive cleaned loads out to restore good hw performance
 