hi i have baxime 105e, hotwater is coming on and off some time,heating is working ok ,pressure is ok, both swiches on valves are working ok,please help me thanks
the problem is that sludge has built up in the secondary heat exchanger, the small one that makes hot water. you should have a magnaclene fitted on the return pipe to the boiler. You will need to replace the secondary heat exchanger to cure the problem, and preferably get the system clean before you fit the new one.