    Good Morning All,


    I have a Baxi Combi 105HE.


    The boiler doesn't appear to be firing when the demand for Central Heating is set to occur.


    If I run a hot tap, the Central Heating LED goes out, the Hot Water LED illuminates and the boiler fires.

    When I close the tap, the Hot Water LED goes out, the Central Heating LED illuminates and any residual heat travels into the radiators (which I assume suggests that the diverter valve is working as it should).


    Could it be a sensor problem or a thermostat (or, even PCB)? Any suggestions how I might test with my meter?


    I'll post a photo of hot water running (whilst central heating should also be on).


    Should the Central Heating LED go out when a hot tap is run?


    Thanks in advance....
     

    Attached Files:

  2. Sponsored Links
  3. wingnut12

    wingnut12

    Joined:
    3 Dec 2018
    Messages:
    3
    Thanks Received:
    0
    Country:
    United Kingdom
    Hi
    Did you ever get this fixed???
    The ch led SHOULD go out when you run you hw, have you checked the micro switches on your diverter valve The rear most on top is you CH, the front one is HW
     
  4. bazdaman

    bazdaman

    Joined:
    2 Feb 2010
    Messages:
    1,380
    Thanks Received:
    316
    Location:
    Lancashire
    Country:
    United Kingdom
    The rear most on top is not a CH micro switch, it proves the pump is running and has to prove on HW and CH
     
    • Like Like x 1
  5. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,431
    Thanks Received:
    8,356
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Wrong there is no CH micro switch
     
  6. Wilson78

    Wilson78

    Joined:
    17 Feb 2016
    Messages:
    30
    Thanks Received:
    0
    Country:
    United Kingdom
    This is from October 2018! Anyway when ever someone says " the back microseitch is the central heating "
    Someone always says " no it isn't "
    At the end of the day it proves the pump etc and it's called the central heating differential valve , so I don't see any issue with it being called the ch diaphragm .
     
  7. Sponsored Links
  8. ianmcd

    ianmcd

    Joined:
    15 Aug 2010
    Messages:
    21,431
    Thanks Received:
    8,356
    Location:
    Lanarkshire
    Country:
    United Kingdom
    Totally wrong, it is the pump proving switch, or primary flow switch it operates on both CH and DHW demand it tells the boiler that it has water and that the pump is running, never a CH diaphragm or CH micro switch
     
    • Like Like x 2
    • Thanks Thanks x 1
  9. Tinkershole

    Tinkershole

    Joined:
    23 Oct 2018
    Messages:
    2
    Thanks Received:
    0
    Country:
    United Kingdom
    PCB fault. Capacitor failed. After troubleshooting the guts, it could only be the PCB mis-firing - it recognised the demand for heating but didn't send the right volts to fire the heat exchanger.

    When hot water was being called for, the boiler fires up and hot water is produced. When switched to central heating, the boiler isn't firing up and any residual hot water, from when it had fired up under hot water demand, passes to the rads. Which tells me that the diverter valve is functioning as it should (I also tested to be sure it wasn't kicking in and out for some reason).

    With everything else functioning, it left only the PCB. £30 exchange at a local electronic shop found on ebay for a re-conditioned board with one year guarantee. Amazing.
     
    Last edited: 21 Jan 2019
  10. Wilson78

    Wilson78

    Joined:
    17 Feb 2016
    Messages:
    30
    Thanks Received:
    0
    Country:
    United Kingdom
    Just a follow up, I'm not making arguments as it seems to have boiled your **** but....doesn't this give my comment any weight?! Just saying! It might not be ch diaphragm as we know it but.... I'll leave it there.
     

    Attached Files:

  11. bazdaman

    bazdaman

    Joined:
    2 Feb 2010
    Messages:
    1,380
    Thanks Received:
    316
    Location:
    Lancashire
    Country:
    United Kingdom
    That's not the boiler he is talking about, that is an instant
     
  12. Wilson78

    Wilson78

    Joined:
    17 Feb 2016
    Messages:
    30
    Thanks Received:
    0
    Country:
    United Kingdom
     

    Attached Files:

  13. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page