Can anyone help, my Baxi boiler failed this week and I need help diagnosing the problem....
Pilot lights and stays lit without problem first time every time.
boiler sits there happily with pilot lit for as long as you like,
When main gas lights I can see through the window that the pilot gets pulled up more into the boiler and does not engulf the thermocouple with enough power to keep it hot, the main gas then goes out along with the pilot.
After this I can re-light straight away and go round the same circle again,
I have removed the pilot injector and can blow through it easily backwards but not easily in the direction of gas flow, is this normal.
Is there any way of adjusting the pilot gas pressure?
Am I on completely the wrong lines and is there anything else I could check? Model is a Baxi Solo WM50 4RS
Any help would be much appreciated,
Thanks in advance,