... whatever I do.
I have a system with Evotouch colour controller and 11 rads.
7 of them have original HR80 wireless TRVs, one a replacement HR92 and 3 plain Drayton TRV4s. These three rely on there being a demand from elsewhere in the system to turn on, this is by design.
ATM the Evotouch is set to Heating Off but the green light on the BDR91 will not go off whatever I do so there is a call for heat all the time. So even if all the wireless zone valves are at 5C the other three rads will be on 24/7.
In line with various other posts I have checked the RF reception on the BDR91 (5 blinks), done a factory reset and re-bound it to the Evotouch controller, all apparently successful but it has made no difference.
I found one of the HR80s was still set to 20C despite being supposed to be off, setting that to 5C by hand has not made any difference either.
Is there anything else I should try?
I have a system with Evotouch colour controller and 11 rads.
7 of them have original HR80 wireless TRVs, one a replacement HR92 and 3 plain Drayton TRV4s. These three rely on there being a demand from elsewhere in the system to turn on, this is by design.
ATM the Evotouch is set to Heating Off but the green light on the BDR91 will not go off whatever I do so there is a call for heat all the time. So even if all the wireless zone valves are at 5C the other three rads will be on 24/7.
In line with various other posts I have checked the RF reception on the BDR91 (5 blinks), done a factory reset and re-bound it to the Evotouch controller, all apparently successful but it has made no difference.
I found one of the HR80s was still set to 20C despite being supposed to be off, setting that to 5C by hand has not made any difference either.
Is there anything else I should try?