phase - neutral = 205
phase - earth = 205
neutral - earth = 50 - or 120 under load conditions
phase - earth = 205
neutral - earth = 50 - or 120 under load conditions


phase - neutral = 205
phase - earth = 205
neutral - earth = 50 - or 120 under load conditions
some idiot repaired a cable in the ground and lashed L1 and L2 to one cable due to an unfound break in L2?
it's been done before...
siroccomanuk said:phase - neutral = 205
phase - earth = 205
neutral - earth = 50 - or 120 under load conditions
If anything gets plugged in to the sockets circuits and switched on (3 seperate rings) the voltage drops to 120 across all circuits.

It will do that through the boding anyway even if the spike is removed (unless all your service pipes are plastic). Anyway it's better that it does that than your earth rising up to 240V relative to real earth.DIDNT disconnect the original TT earth spike when it was upgraded to TNC-s at the same time so neutral was 'leaking' to earth when the wind blew! Bloody dangerous.