Hi All,
We have a Vokera Mynute 16e boiler in an s-plan system to give independent control of the hot water and heating.
When the system is calling for heat for the hot water cylinder only we find that the boiler cycles rapidly - 30 seconds burn, couple of minutes rest, over and over again until the cylinder stat is satisfied. Throughout this time the call for heat is constant - so I'm assuming it's because the coil in the cylinder isn't transferring the heat quickly enough to provide a significantly cooler return to the boiler? If you turn on the heating at the same time the cycling reduces greatly - doesn't go away totally but I've not made any attempt to balance the radiators yet.
Tank it's self is, I think, rather small - about 90 litres, so I would have thought it should heat fairly quickly - it takes best part of an hour of this cycling to get us back to 60c in the morning following overnight cooling.
I suspect given the quality of the fit-out of the house in other areas that the cylinder is the cheapest thing that the developers could get their hands on - they didn't even put in proper heating controls - we've done that. They also decided not to fit a drain point in the system too - very helpful!
Anyway, I'm not a gas engineer but I don't think our boiler is capable of modulating it's flame - I think it's all or nothing. Do we need to get a gas engineer in to tame the boilers output a bit, or would a better cylinder with a fast recovery coil be the way to go, or is this the way it's supposed to be and we should just leave it alone?
Cheers
We have a Vokera Mynute 16e boiler in an s-plan system to give independent control of the hot water and heating.
When the system is calling for heat for the hot water cylinder only we find that the boiler cycles rapidly - 30 seconds burn, couple of minutes rest, over and over again until the cylinder stat is satisfied. Throughout this time the call for heat is constant - so I'm assuming it's because the coil in the cylinder isn't transferring the heat quickly enough to provide a significantly cooler return to the boiler? If you turn on the heating at the same time the cycling reduces greatly - doesn't go away totally but I've not made any attempt to balance the radiators yet.
Tank it's self is, I think, rather small - about 90 litres, so I would have thought it should heat fairly quickly - it takes best part of an hour of this cycling to get us back to 60c in the morning following overnight cooling.
I suspect given the quality of the fit-out of the house in other areas that the cylinder is the cheapest thing that the developers could get their hands on - they didn't even put in proper heating controls - we've done that. They also decided not to fit a drain point in the system too - very helpful!
Anyway, I'm not a gas engineer but I don't think our boiler is capable of modulating it's flame - I think it's all or nothing. Do we need to get a gas engineer in to tame the boilers output a bit, or would a better cylinder with a fast recovery coil be the way to go, or is this the way it's supposed to be and we should just leave it alone?
Cheers