Boiler doesn’t ever click off

Joined
14 Oct 2026
Messages
1
Reaction score
0
Country
United Kingdom
Hi all

Weird thing not sure if it’s always been like this but here goes

Boiler doesn’t ever seem to cycle the burner while it’s running, it seems to stay lit constantly and the silver flue block outside steams the entire time the heating is on

If it’s set to hot water only it does turn off after an hour or so

Is this normal? It doesn’t ever seem to overheat and seems to work extremely well

It’s a Glowworm hideaway apparently, it seems quite old but seems to work very well indeed

I think it’s gravity hot water as there’s no 3 port valves I can see and pumped heating with 13 radiators, all are red hot and evenly heated

Thanks
 
I have looked at the instructions and it does say
1794879041955.png
but it does not show how these should be installed, no wiring diagram.

Maybe you can give a little more info.
 
With 13 rads all running hot, that's quite normal. The house is soaking up everything the boiler makes. So the water never gets back up to the boiler stat temperature, and the burner just stays on.

Steam from the flue is normal on a cold day. It's just water vapour in the exhaust.

Do you have a room thermostat anywhere? If not, the boiler only stops when the timer goes off. That's why it never cycles on heating. On hot water only, the load drops once the cylinder is hot, so it shuts off.

A room stat and TRVs on most rads would save you a fair bit of gas.

On a boiler that age, make sure it gets a yearly service. Put a CO alarm in the same room as the boiler too.
 
Boiler doesn’t ever seem to cycle the burner while it’s running, it seems to stay lit constantly and the silver flue block outside steams the entire time the heating is on
That's normal, the rads dissipate the heat so the boiler doesn't reach control-stat setting. So it fires until the roomstat or the programmer stops it.
If it’s set to hot water only it does turn off after an hour or so
The cylinder can't take the boiler heat output, so the temperature rises to the control-stat setting. But if it's a very basic system with no 3-port valves or cylinder stat, it's using gas all the time it's in HW only mode, just to keep the boiler hot, and convection through the boiler quickly cools it. Well worth upgrading to one of the C-plans, depending how much work you want to do.
 