Boiler stat still set to Max, yes?
To find out if the fault is with the boiler or the external controls you need to know whether demand from the room stat is providing a switched live to the boiler via the MV by connecting a voltmeter to boiler SWL terminal.
"Boiler on" light; is that a demand light from room and/or cylinder stats or a light to tell you that the main burner is firing?
To find out if the fault is with the boiler or the external controls you need to know whether demand from the room stat is providing a switched live to the boiler via the MV by connecting a voltmeter to boiler SWL terminal.
"Boiler on" light; is that a demand light from room and/or cylinder stats or a light to tell you that the main burner is firing?