Boiler not firing for CH - duff roomstat? Theben Ramses 811
23 Sep 2008
Hampshire
Hi
I am having issues with getting my ancient (Gloworm Fuelsaver F) conventional boiler to fire up for central heating. When the room stat - (a Theben Ramses 811 top1) has been turned up and heard the audible 'click' the boiler does nothing. DHW is running fine and the tank thermostat fires the boiler fine.
I initially thought I had a faulty programmer (an original Drayton Switchmaster 805) which I have now replaced with a Drayton LP241. The programmer seems to work fine, I can turn HW heating on/off via the programmer fine.
The room stat has a 2-wires connected so I'm hoping to find a cheap compatible replacement.
The manual for the current room stat is
http://www.theben.de/var/theben/sto...instructions_RAMSES811top_RAMSES812top_en.PDF
Any help would be very much appreciated. Is it possible to override the room stat and force CH 'on'?
Cheers
As an aside, I noticed that when the boiler is on for HW heating the radiators warm up - is this the norm?
Connect both wires together at the room stat. This should mean the CH will be on constantly and will confirm if the stat is at fault.
Motorised valve looks to be most likely suspect.
Kinda rules out the room stat. Do you have any motorised valves?
Hi, yes there is a motorised valve in the airing cupboard. The lever seems to be in the 'auto' position. It moves very freely up/down with no audible click or any change from the boiler end.
Here's a (bad) photo :