Ok. FCU to boiler on. Water and CH set to constant.
At Boiler:
230v between ON and Live.
0v between ON and Neutral.
0v between ON and Earth.
then you don't have a demand at the boiler then
the fault lies with the external controls
Matt
Ok. FCU to boiler on. Water and CH set to constant.
At Boiler:
230v between ON and Live.
0v between ON and Neutral.
0v between ON and Earth.
Will anymore photos help out?
The SL from room stat goes to the 10 way j/box. it is connected in the connector strip with the white cable from the sundial Y diverter.
The SL from room stat goes to the 10 way j/box. it is connected in the connector strip with the white cable from the sundial Y diverter.
Re my earlier post.
orange and white wires are found on the mid-pos valve
mid position valve wiring. CH turned on
White wire to earth/neutral (230v) indicates heating demand to valve
Orange wire to earth/neutral (230v) indicates power to pump/boiler
Re my earlier post.
orange and white wires are found on the mid-pos valve
mid position valve wiring. CH turned on
White wire to earth/neutral (230v) indicates heating demand to valve
Orange wire to earth/neutral (230v) indicates power to pump/boiler
ok. I have a plumber coming tomorrow to look at it. I will call him in the morning to see if he can replace parts rather then the whole thing.