That's brilliant.. don't suppose your an expert on TRV's too are you? So grateful for your help mate..!
Most TRVs jam internally one time or another severely restricting the flow of water through the radiator. They are all similar in construction/problems. Remove the head (undo the securing ring/screw clip/whatever). Underneath you'll see a pin about as big as a biro nib, DO NOT PULL THE PIN UP! It should have approx 3-4mm of travel up and down. Use a spanner or flat tool to press on the pin with your hand to see it theres any movement. If there is keep pushing down and then let the valve spring back up till you get it free as possible. If the pin is stuck GENTLY tap the pin SQUARELY on the end to free of the stuck mechanism in the valve body. Don't get too heavy handed as you'll burr the end of the pin or bend it, then its new valve time. You can do all of this with the heating on, as hopefully you'll feel the hot water come through as it frees off.
If the TRV is over 15 years old change it anyway! The sensor head is probably well out of calibration and the body may stick again soon. Good luck