Boiler pressure keeps increasing

Discussion in 'Plumbing and Central Heating' started by mk85, 26 Jul 2014.

  1. mk85

    mk85

    Joined:
    19 Feb 2007
    Messages:
    25
    Thanks Received:
    0
    Location:
    London
    Country:
    United Kingdom
    -Vailant combi boiler – ecoTEC plus 824
    -Boiler is 3 years old.
    -The Cold Water-in valve has a flexi hose which is connected to the CH Flow pipe. There are 2 grey knobs on the flexi hose valves which both need to be opened a quarter turn to increase CH boiler pressure.

    Last week I noticed the boiler pressure had dropped to 0.6bar. I increased the pressure to 1.2bars while the heating was off, by turning both the grey knobs.

    A week later I noticed the pressure had increased to 2.8bars. I bled a radiator so that the pressure reduced to 1.2bars. 2 days later the pressure had increased to 2.5 bars.

    (NOTE – Both the knobs on the flexi hose were in the closed position after refilling – and double checked on both occasions.)

    Again I bled a radiator to reduce the pressure to 1bar this time. I also disconnected the flexi-hose from the CH Flow pipe end only.

    I noticed a small drip from the flexi hose (1 drip every 10 seconds) AND a small drip from the CH Flow valve (1 drip every 3 seconds)

    I took the grey knobs off and used a pair of pliers to make sure both the Cold Water-in and CH Flow valves were totally tight in the closed position.

    But both drips have continued. What is the likely problem? and what would be the solution?
     
  2. oldbuffer

    oldbuffer

    Joined:
    6 May 2010
    Messages:
    1,435
    Thanks Received:
    535
    Location:
    London
    Country:
    United Kingdom
    Sounds as if both valves are letting a small amount of water past, even in the closed position. This would account for the rise in pressure before disconnecting the filling loop. Only real solution is to replace both valves. Get good quality ones, not cheap ones. It will require turning the incoming cold water off at your main stopcock and draining down the system (unless you can freeze the boiler flow).

    You might wish to consider re-installing the filling loop between the cold inlet and the boiler return pipe, as the return is cooler than the flow, and the valve may last longer. If doing that, don't forget to blank off / remove the old connection to the flow.
     
  3. Sponsored Links
  4. MANDATE

    MANDATE

    Joined:
    6 Mar 2003
    Messages:
    2,328
    Thanks Received:
    134
    Location:
    Manchester
    Country:
    United Kingdom
    I witnessed a valve a few months back that had been turned off (with filling loop disconected)fully to the stop, it leaked and pressure reducing. Obvious solution was a replacement valve.
    Then found by turning clockwise a very small amount the leak stopped and pressure stable
     
  5. Bunnyman

    Bunnyman

    Joined:
    22 Mar 2010
    Messages:
    5,497
    Thanks Received:
    1,841
    Location:
    Northamptonshire
    Country:
    United Kingdom
    A known prob I'm afraid change valve 0020010295
     
  6. Sponsored Links
  7. Bunnyman

    Bunnyman

    Joined:
    22 Mar 2010
    Messages:
    5,497
    Thanks Received:
    1,841
    Location:
    Northamptonshire
    Country:
    United Kingdom
    Just change the valve an stop fookin about :rolleyes:
     
  8. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page